Does it make a difference which neutral bar that I use?

Posted by uniflow (My Page) on
Fri, Dec 7, 12 at 22:46

My 200A QO entrance panel has two ground/neutral bars, one on each side next to each 120V leg breaker stack. Most of the branches enter the left side but four of them for lack of available breakers on the left leg are landed on right leg breakers. My question is are both ground/neutral bars strapped? In order to make the box neater and shorten the wires may I land grounds and neutrals on unused taps on the left ground/neutral bar even though the hot is on the right leg? If the bars are just bonded to the panel but not strapped to each other I am concerned about putting potential on the box. I would think the bars must be strapped to handle unbalanced 240V loads though.
Thanks for your help, Jim


Follow-Up Postings:

 o
RE: Does it make a difference which neutral bar that I use?

Hold the phone here. Which bars are we talking about?

If we are talking about the ones on the plastic standoffs up by the main breaker, they are electrically equivalent and you can connect the neutrals to whichever one you want. If the bonding screw is installed (i.e., this is the service disconnect), you can also land your grounds there.

If you are talking a bar lower down by the breakers that is screwed directly to the case that is ALWAYS a ground bar. You can not land neutrals there.

QO panels come with only the combined neutral/ground bars on the plastic standoffs. There's a screw that bonds this to the case if this is a main panel. If you want to use this as a subpanel, then you take that screw out and you have to mount a seperately sold ground bar to the case. There are tapped, raised holes for this on both sides. You can install one on either side or both.


 o
RE: Does it make a difference which neutral bar that I use?

ronnatalie, Thanks for the reply. This is the entrance (service disconnect) panel and the bars in question are definitely neutrals/grounds. I know what you are saying about dedicated grounding bars to the case (I had to put one in my incorrectly wired out building to separate the neutrals from grounds), but the entrance panel has no separate ground bars. And being the main breaker the bonding screw is in place.
Thank you again for the answer.


 o
RE: Does it make a difference which neutral bar that I use?

Land the neutrals and grounds for each circuit adjacent to the breaker the hot is landed on.

If the breaker is very near the cable entrance to the panel, leave some extra wire folded back on itself.

While some of the jobs look very 'neat' with direct runs of minimum length, they turn into a nightmare as soon as anything needs to be moved.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here