Question on AC condenser unit
| | |
Posted by
lesliew (
My Page) on
Sun, Dec 19, 10 at 21:13
| My home has three phase wiring, and last year, when I had to replace a five ton AC condenser, the AC company told me I either had to use a three phase unit (commercial, and more expensive), or they would have to redo the wiring. I told them I would prefer not to jury rig the wiring, and wound up spending almost five thousand dollars for the unit. I had a smaller unit replaced this year, by another company, which turned out to be single phase. When I mentioned my relief, and told the guy the story about the larger unit, he looked at it, and said it was single phase. I went back to my contract, and checked out what was written, and it definitely said three phase, thirteen seer. I checked the model number online, and found it to be a single phase, eleven seer unit. Obviously the installer took me for a ride, but my main question is - what did they have to do to the wiring to use a single phase unit, and should I be concerned about the wiring, as wlel as about the fraud involved? |
Follow-Up Postings:
RE: Question on AC condenser unit
| | |
| Probably only had to cap the unused third phase wire. |
RE: Question on AC condenser unit
| | |
| If you wire across two phases of a 3-phase circuit, won't the resulting waveform be a bit whacky? The two phases are 120* apart, not 180*, so won't the voltage be non-steady? |
RE: Question on AC condenser unit
| | |
| Using two legs of a three-phase system is simply single-phase. there is no problem with the voltage. Two legs of a 120/208V 3-phase system is 208V. |
RE: Question on AC condenser unit
| | |
| If you wire across 2 phases, you'll typically have a "steady" 208V. Whether or not the AC will run on that is another question. Unless designed for that voltage, my guess is that the lifespan will be shortened considerably. |
RE: Question on AC condenser unit
| | |
| A delta service was once quite popular for larger residential HVAC installs. If it is a 120/240 delta service, a wire nut cap on the "wild leg" makes it essentially the same as 120/240 single phase. Since the circuit capacity will be lower that way, my advice is to find a reputable HVAC company to look over the install. Then take that information and your contract to a good, mean lawyer. Fraud seems fairly common in the HVAC trade, when I had a unit installed, a 2 ton condenser was "accidentally" placed in the carton marked as 2.5 ton. |
Post a Follow-Up
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in.
If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.