GFI Install and no voltage over .1?
| | |
Posted by
dan261s (
My Page) on
Tue, Dec 22, 09 at 20:22
| I've successfully installed 2 GFI outlets on other circuits for bathrooms however aren't able to install one in my kitchen. Two 12/2 cables are coming into the gang for the outlets line and load however unlike the other two gfi outlets and all i've ever seen, both of the wires black/white are only reading .1 volts? Is this possible? I imagine their is some sort of short somewhere as when both wires are hooked up to a normal recepticle, it correctly reads a little over 120. I've hooked up multiple GFI's to the wires thinking it could be the GFI and even reversed the load and line wires as one way does show the green light that it has power but won't reset suggesting its backwards but nothing seems to work.
Any ideas or assistance is extremely appreciated! Thanks |
Follow-Up Postings:
RE: GFI Install and no voltage over .1?
| | |
| bad GFCI outlet or it is tripped. press the reset button, if still no voltage then verify you have 120v on the screws. maybe you trippe dth ebreaker or did not fully turn it back on after the swap out? |
RE: GFI Install and no voltage over .1?
| | |
The last one I installed came 'tripped' right out of the box. After installation and power is supplied, it can be reset. After a lot of head scratching I discovered this,(after reading the instructions). |
RE: GFI Install and no voltage over .1?
| | |
| Could be as simple as a bad GFCI. Basic troubleshooting would be to ensure 120v supply. Connect line side (make sure the hot wire is attached to the brass colored screw), test. Connect load, test. |
RE: GFI Install and no voltage over .1?
| | |
| I'll reset the breaker and test the voltage again however on my last attempt when each line isn't connected to the gfi, each white/black combination were only reading .1 volts. Once on the GFI, their was no reading. The strange part is when both lines reading .1 are hooked up to a normal recepticle, they correctly read around 120v. |
RE: GFI Install and no voltage over .1?
| | |
| I'll reset the breaker and test the voltage again however on my last attempt when each line isn't connected to the gfi, each white/black combination were only reading .1 volts. On multiple GFI's hooked up, i was never able to reset. Once on the GFI, their was no reading. The strange part is when both lines reading .1 are hooked up to a normal recepticle, they correctly read around 120v. Since this wiring is original to the house built in "65, i'm thinking something is crossed somewhere? |
RE: GFI Install and no voltage over .1?
| | |
| It's possible you have a ground fault as well, perhaps a ground-to-neutral connection downstream (this is likely if things trip when there is no actual load connected). |
RE: GFI Install and no voltage over .1?
| | |
| Problem fixed - Disconnected ground wire had run to basement water pipe which was somehow causing the 0.1 volt reading. Understand this is allowed for a GFI without ground hookup as long as correctly labled. |
Post a Follow-Up
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in.
If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.