| We have found a new oven and I believe it might work. We have 240v on 10-3 wire with 30 amp breakers.The new oven specs are; total connected load: 6.8KW @ 240v, amp rating at 240v-30amp. Will this work?? Thanks for the help to anyone that answers. |
Follow-Up Postings:
|
| Yes, assuming that it's copper wire, everything should be fine. 6.8kw converts to 28.3A. |
|
| You will want to check the oven's installation instructions to make sure that a 30 amp breaker / circuit is called for. |
|
| "Yes, assuming that it's copper wire, everything should be fine. 6.8kw converts to 28.3A." Except that would load a 30 amp circuit to over 94%. It might be acceptable if the installation instructions call for a 30 amp circuit, otherwise you may need a little more. |