I'm wiring up some baseboard heaters using 12 ga cable. I have been told that 12 ga cable won't safely take
more than 16 Amps....
I have also been told that 12 ga cable on a 25 amp breaker
is fine for 4800 watt baseboard heaters....20 amps

Which is correct.
Thank you


Follow-Up Postings:

 o
RE: Amperage

#12 AWG can only be used with a maximum circuit breaker of 20 amps. Whoever told you 25 is WRONG.
As for the 16 amps. 16 is 80% of 20. You can only load a circuit to a maximum of 80% of the over current protection rating.

if you have a 4800 watt heater using 240 volts that comes to 20 amps. you HAVE to pull #10 AWG to it and use a 30 amp breaker.


 o
RE: Amperage

hexus..our code (Canada) says they have changed the rules allowing higher rated breakers to make greater loading possible. Allowing a 25 amp breaker for 4800 watts.
Why they allow this I don't know.

Would you suggest I ignore the code, if I use 12 ga cable, and go with 20 amp breakers loading only to 16 amps?


 o
RE: Amperage

Just some clarification:

"#12 AWG can only be used with a maximum circuit breaker of 20 amps. Whoever told you 25 is WRONG."

There ARE some instances where #12 can be on a 25A breaker, but they do not apply here.


"As for the 16 amps. 16 is 80% of 20. You can only load a circuit to a maximum of 80% of the over current protection rating."

This is not true in most instances. You certainly CAN load a circuit to 100%.
Continuous loads though, or those considered continuous loads such as electric heat, DO have to be kept to 80%.


That said, I am not familiar with the Canadian code on this so I won't comment further on that.


 o
RE Amperage

I have no clue on Canadian codes. My mistake I assumed you were in the states.


 o
Amperage

I don't know why they changed the code..which used to be the same as yours in this case but I think i'm going to go with your advice...
Our code seems a little too liberal for me.
Thanks for the responses...appreciated


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here