| I will be running 3 AWG 120/240 feed to my out building. What size should the ground wire be? |
Follow-Up Postings:
|
- Posted by petey_racer (My Page) on Thu, Dec 1, 11 at 20:28
| I assume 100A, so #8cu. |
|
- Posted by Entlebucher (My Page) on Fri, Dec 2, 11 at 19:21
| I would like to thank all of the responders for their valuable advice which I intend to take. To answer darrelectric's question, the run is about 165 ft. I would also add some history to my problem. I originally had a 4 wire system using #4 AWG run in 2" conduit to this out building which serves as a workshop. This system was fed by a 50 amp breaker from a 100 amp sub panel. During our latest power outage I back fed the house using a 7 Kw generator thru the workshop panel. Some time after the power was restored,one phase failed. I can not pull the old lines out of the conduit so I intend to run new lines and conduit using heavier #3 wire so that I can run a 13 Kw generator in the future. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.