Subpanel for an unattached building

Posted by Entlebucher (My Page) on
Thu, Dec 1, 11 at 18:02

I would like to install a subpanel in an out building. I plan on running individual conductors in PVC conduit. Can I run 2 hot leads and a neutral to the subpanel and use a ground rod at the out building instead of running a ground wire in the conduit?


Follow-Up Postings:

 o
RE: Subpanel for an unattached building

Depends what version of the electrical code your jurisdiction is operating under. Frankly, it is a very very good idea to do so even if you're on one of the older codes anyway.

If you're running more than one circuit in the outbuilding you will require a grounding system (which is probably more than ONE ground rod).


 o
RE: Subpanel for an unattached building

I wouldn't think there is any area left in the US still under the 2005 NEC, which allows the use of the neutral to also serve as the ground in some cases like this.

Entlebucher, you need two hots, a neutral AND an equipment ground conductor.
A ground while is required in either case, but has nothing to do with equipment grounding. It does not take the place of one nor does it serve nearly the same purpose.


 o
RE: Subpanel for an unattached building

Missouri (other than St. Louis),DC, Utah, and Connecticut appear to still be on 2005. Many of the major cities in areas that haven't got statewide adoption are still there: including Tuscon, Springfield, IL, most of Maine, a good deal of Maryland, etc...

That being said, if you have any metallic connections to the building other than the power, you can't use the exemption either. As I stated, even if you qualify (old code, no other metallic paths) it's still a really, really, good idea to run the ground between the structures.


 o
RE: Subpanel for an unattached building

Don't forget to drive 2 ground rods at least 6ft apart as well. That is unless you can verify that the resistance to ground from only one rod is within specs.


 o
RE: Subpanel for an unattached building

why not run all 4 wires?
and a ground rod for the ground near the remote panel.

running all 4 wires will guarantee the voltages will in reference to each other. and all the conductors that are intended to carry current--carry current. and those that aren't supposed to carry current DON'T.

the additional ground rod will add to the lightning protection...what happens if a bolt hits your out building..what's the current path to ground? back up the wire to your house? might not be a good plan.

-dkenny

ps..it it were me..i'd run 4 wires out to the out building.
but that's me.


 o
RE: Subpanel for an unattached building

Thank you Dkenny. You just got around to saying exactly what I said in the very first post. One rod itself is not likely to be an effective and legal ground.
It's highly advisable to run the grounds between the buildings. However, to assuage the pedantic here, there are still large chunks of the country that in certain situations you can legally get away with not running it. The major reason to do so would be COST.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here