Posted by scottys (My Page) on
Mon, Dec 28, 09 at 14:17

I am installing central ac for the first time and I am running the line myself. Do I need a fusible or non-fusible ac disconnect switch for my outdoor condenser
unit? The 220v unit will be fed by #10 wire protected by a double 30amp breaker located in the main panel.
Does the fusible switch offer a measure of "extra" protection? or would i be better off with the more compact and cheaper non-fusible disconnect?
Thanks.


Follow-Up Postings:

 o
RE: Central AC disconnect

The local disconnect is simply that -- a disconnect. It does not need to be fused and there is no compelling advantage to buying a fused disconnect. A cheapie should be fine here.

[BTW, have you checked the manufacturer's specific recommendation on the breaker size? The reason I ask is that AC units are sometimes fused at the max amps rating to accommodate the starting surge of the compressor whereas the wire is sized according to the minimum circuit. This may be a case where you can use #10 wire on a 40A breaker, so doublecheck that rec' before buying the breaker.]


 o
RE: Central AC disconnect

"It does not need to be fused and there is no compelling advantage to buying a fused disconnect. "

In some jurisdictions it won't pass code enforcement without one!


 o
RE: Central AC disconnect

Just so I'll know for future reference, where, exactly, are a few of these jurisdictions located? Is this a commonplace local code modification in some region or another? Does it apply to residential applications?

Alternatively, if the "code enforcement" is based on the NEC, what's the code cite used to disapprove an unfused disconnect? (Notwithstanding the obvious case where additional overcurrent protection is needed at the point of a disconnect fed from an oversized circuit.)

Has anyone else run into this problem?


 o
RE: Central AC disconnect

I've never run into the requirement for a fusible disconnect in addition to a protected circuit. One of the counties here in Maryland (Anne Arundal County)has some of the most stringent local requirements in addition to NEC, in the country and the only requirement for a disconnect is, a lockable disconnect at the condensing unit.


 o
RE: Central AC disconnect

... There are some units whose manufacturers specify FUSE. This is the case when a fused disconnect will be required.

ie, your A/C unit states "30A Fuse or circuit breaker" = no fused disconnect required. However, if it states "30A FUSE", one IS required.


 o
RE: Central AC disconnect

"However, if it states "30A FUSE", one IS required."

Yep, that makes sense to me, Mike. If a manufacturer specifically calls for a fuse then I reckon you'd have to follow that instruction. What complicates matters, I suppose, is that the term "fused disconnect" is also commonly used to include disconnects with breakers. Similarly, a topical heading like "Fusing" often refers to overcurrent protection in general, whether by breaker or fuse.

(BTW, I wasn't aware of manufacturers who specifically require fuses for small residential A/C units these days. But if they're out there, I agree with you.)


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here