Bathroom Heat Lamp and 12-3 question

Posted by tom_p_pa (My Page) on
Sun, Dec 3, 06 at 8:46

I was in Lowes buying recessed lights, and was also looking for a heat lamp housing. Is there a special housing for a heat lamp, they had the bulbs (250 Watt). And regular recessed light housings had a 75 watt limit.

Can a 12-3 wire cable be used as really 2 circuits. I am running some new circuits to some rooms I am redoing and someone at work said to run one 3 wire romex and use that as 2 circuits. I am trying to split us the rooms that are all on one 14 2 wire circuit and the breaker keeps tripping (2 bathrooms, the washer dryer, and the basement). I plan on running one 12 wire circuit to feed the washer dryer, and one 12 3 wire cable to feed the 2 bathrooms.


Follow-Up Postings:

 o
RE: Bathroom Heat Lamp and 12-3 question

NO, you cannot use regular recessed cans as heat lamps. You need a heat lamp fixture. Most have a fan built in with a thermal cutout so if it gets too hot either the light goes off or the fan comes on.
Bath fan companies make them.

Yes, you can use 12/3 to run two circuits.
NO, you cannot re-feed a 14/2 circuit with the #12 and use a 20 amp breaker. Using #12 would be a waste.
Just leave the existing as is and run new circuits to where you need them.


 o
RE: Bathroom Heat Lamp and 12-3 question

Regarding using a 3 wire to supply 2 new circuits to bathrooms being gutted..I just read another post where the GFCI keeps tripping because it shares the same neutral. Is this going to be my situation that I will have 2 bathrooms with seperate circuits being feed from the same neutral on the 3 wire. I did not fully understand the post. If this is the case, can I install a GFCI outlet in the bathroom, does this eliminate this problem? I will have a bathroom light and fan over the shower too which I need to get into the GFCI circuit.


 o
RE: Bathroom Heat Lamp and 12-3 question

If you split the circuits to two 12/2 feeds you can do as you wish after that as far as GFI devices. There will be no tripping problems.

The fan over the tub should be GFI protected only because the manufacturer most likely requires it. There is no GFI requirement for recessed lights or fans OVER tubs. Only that we follow mfg instructions.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here