Do I need to replace this wire?

mikec205
13 years ago

I want to replace and old style screw in fuse box with a new 100a service panel to a detached garage. The Main feeder wire is probably from the 50's - 60's it is not romex. It is two large gauge wires wrapped with an outer ground wire and then encased in some type of plastic casing. The wire is copper but appears siver until you scratch it. So there are a total of 3 wires.

To replace all if it with thhn would be really expensive. What are my options here? Can I use the existing wire or does it need to be upgraded to work with the new service panel?

Comments (6)

  • mikec205
    Original Author
    13 years ago

    Did some searching and found that it is un grounded romex from the 1950's it looks similar to this photo

    Here is a link that might be useful: photo

  • DavidR
    13 years ago

    This cable you describe is feeding your detatched garage??? Is it buried? In conduit underground, or buried unprotected? Flown overhead? Please provide further details. Photos of your actual installation would help.

  • Ron Natalie
    13 years ago

    If it's really 14g as you mentioned on the other site there is *NO WAY* you can run 100A service on this stuff. Let alone that it is missing conductors needed to do this safely and legally by the current code. You need to use appropriately sized and rated conductors (for conduit) or cable (appropriate to whatever installation this is as alluded to by davidr)... which is going to be at LEAST #6 with four conductors.

  • terribletom
    13 years ago

    I'm having difficulty reconciling the photo with your description, i.e., "two large gauge wires wrapped with an outer ground wire and then encased in some type of plastic casing."

    Ignoring the photo for now, my hunch is that the cable is old-style "SE", not the type of "Romex" used for ordinary house branch circuits. And if it's typical of the time period you surmise, it most likely consists of two #6 conductors (one red, one black) covered with a braided neutral/ground under a plastic sheath or cloth sheath impregnated with a water-resistant binder.

    In the past, outbuildings such as garages were very commonly fed by three-wire cables with the two insulated conductors used as hots and the braided bare wires serving as both neutral and ground. In fact, three-wire feeds to independent outbuildings were perfectly legal for new installations up until the 2008 code revisions (with a few specific restrictions, such as a requirement that there be no other metalic connections between home and outbuilding). This wiring method is no longer legal for new installations or major renovations.

    In any case, I'd be quite surprised if the conductors are larger than #6 and, if that's the correct size, it could in no way carry more than about 55 amps safely, even under older versions of the code.

  • mikec205
    Original Author
    13 years ago

    Terrible Tom's description of the wire is accurate it's probably about a #6 wire with a braided bare wire. Sounds like I'll need to replace all of it $$$$$$

    Thanks for the replies

  • smithy123
    13 years ago

    I would replace it.