| Our laundry room has two 120V receptacles, one for the washer and another one on the opposite wall on the same circuit. Both are non GFCI. We are installing a laundry sink, cabinets and countertop next to the W&D on the same wall and would like to have another receptacle on that side of the room also.
Can we tap into the existing circuit to add the extra receptacle? I was under the impression that the washer was supposed to be on its own dedicated (GFCI?) circuit. Thanks for any input. |
Follow-Up Postings:
|
| yes you can do that as it will in the same laundry room. You only are going to need to GFI them if they're 6 feet or less from the outer edge of the sink. |
|
- Posted by bus_driver (My Page) on Thu, Nov 12, 09 at 18:56
| A washing machine does not have to be on a GFCI. In fact, the washer might cause nuisance tripping of the GFCI. Yes, you can add receptacles in the laundry room from the existing circuit. And it might be wise to cease accepting electrical wiring advice from your previous sources. |
|
| "And it might be wise to cease accepting electrical wiring advice from your previous sources." that made me laugh, however for some reason GFI protecting the washer receptacle seems to be something people struggle with. I have one state inspector in one area I do work in that insists that we have to GFI it. I've tried arguing and finally decided it's not worth it and always just have to remember to throw in an extra GFI on the trim. |
|
- Posted by tom_in_seattle (My Page) on Thu, Nov 12, 09 at 19:30
| Well, what if the washer receptacle is less than 6 ft from the sink? Is it still "exempt?" Maybe I should switch that from a duplex to a single receptacle. When we add the laundry sink then the current extra receptacle and any others we add will need to be GFI protected because they will be within just a few feet of the sink. Thanks for clearing up my question whether the washer needed a dedicated circuit. I thought I read that in this forum, but it was probably that the laundry room needed to be on a dedicated circuit. |
|
- Posted by petey_racer (My Page) on Thu, Nov 12, 09 at 19:37
| Hexus IS right, under the 2008 NEC. Any exceptions to the GFI rules for laundry rooms and basements have been removed. Tom, the "laundry" needs a circuit, not the washer alone. As the others said, you CAN add a receptacle to this "laundry circuit". |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.