outlet wiring problem

Posted by mavic (My Page) on
Mon, Nov 4, 13 at 17:18

Hello,

I have two outlets not working. There is power to the black positive wire but not to the white negative must be loose somewhere. However, the third copper ground wire is good and I get power if the positive and this ground wire is used.

Question, is this safe to use the copper ground wire as my negative wire?

TIA!


Follow-Up Postings:

 o
RE: outlet wiring problem

OK, in AC building wiring there is NOT pos and neg.
There is a hot and a neutral. The ground is NOT a current carrying conductor and it is ABSOLUTELY NOT safe to use as a neutral.


 o
RE: outlet wiring problem

Start from the two outlets that are not working, go to the next one that is working and look there for a loose neutral. As Petey points out the bare/green ground is not designed to be carrying current. It's there for safety.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here