Going from a 14/2 to 14/3

MsGreen1
12 years ago

I replaced my bathroom lights and messed up the wiring downstream. The power source is a 14/2 coming directly into one of the two light fixtures. From there, I hooked up the other light and in the opposite direction used a 14/2 to connect to the 14/3 going to the switch. I wired the black to the black and red, and the white to white. The 14/3 goes into the switch box, where I tied the black to the black from the switch, the red to the black of the out-going 14/2 (power going out to 2 other rooms), and the white to the white on the switch and the white from the out-going 14/2. I obviously messed up because, though my 2 lights I installed work beautifully, the rest of the circuit is not right. Help!

Comments (3)

  • kurto
    12 years ago

    I'd need a drawing or pictures to understand precisely what is connected to what. What's not clear is what happens to the other end of the white wire that you're using as part of the switch loop. It's quite clear that it can't be connected to both the switch and the neutral of the remaining circuit at the same time.

  • esobocinski
    12 years ago

    I think I understand the question.

    Old situation:
    - Power entered an old light box via 14/2.
    - There was a 14/3 from that box to the switch.
    - The black and white to the switch supply outlets downstream of the switch.
    - The switch was connected between the black and red.
    - The old light was connected to the red from the 14/3 and the combined white. The switched power to the light traveled 'backward' along the red to the light.

    New situation:
    - The old light has been replaced in a remodel.
    - There's a 14/2 from the new first light to a second light.
    - MsGreen1 has extended the 14/3 to the new first light box with 14/2, disconnected the 14/3 black from the upstream power and connected it to the 14/2 extension black that is connected only to the lights.
    - The outlets downstream of the switch are now fed by power *through* the lights when the switch is off, and so they never work right. When the switch is on, they're shorted entirely out of the circuit.
    - Guessing: The switch is now probably connected on the neutral side of the lights, which is just plain wrong, and potentially dangerous when changing bulbs.

    The only solution is that you need to remove that 14/2 extension of the 14/3 and replace it so that you have 14/3 all the way from the first light to the switch. Connect it so that:
    - All whites are connected together in each box
    - The 14/3 black is connected to the power source black
    - The 14/3 red in the box of the first light is connected to the light fixture black
    - The 14/3 red is also connected to the black wire of the 14/2 going to the second light.
    - The switch box is reconnected the way it was, with white-to-white, black-to-black, and the switch between blacks and the 14/3 red.

    I don't have time to draw right now, but here's a picture from someone else. You'll have to imagine connecting the cable to the second light in the same places that the light shown is connected.

    Here is a link that might be useful:

  • MsGreen1
    Original Author
    12 years ago

    esobocinski: you are absolutely right, on both counts. I sent a diagram to an electrically gifted friend, and his response was the same as yours. Thanks for the help! And no worries, I won't be using that circuit until I get it wired right, so no fires. Thanks!