| Just wondering if anyone could give me the price to install at natural gas standby generator (just the installation, not the generator itself)
Thanks. |
Follow-Up Postings:
|
- Posted by petey_racer (My Page) on Tue, Nov 8, 11 at 16:34
| Considering the glaring lack of details given, I'd say $500-$2500 |
|
- Posted by ronnatalie (My Page) on Tue, Nov 8, 11 at 17:09
| Does the house already stand? What size generator? Will it serve the whole house? Will there be an automatic transfer switch? I'd put it under $1000 to site the generator and install the gas line, but the amount of electrical work involved varies widely. |
|
- Posted by growingadvice (My Page) on Tue, Nov 8, 11 at 19:18
| Tying in to the main box in existing home Probably 15kw, I'm guessing whether it's 5kw or 25kw, the price physical connection to the box would likely not vary greatly. The size of the generator itself is essentially the same. |
|
- Posted by growingadvice (My Page) on Tue, Nov 8, 11 at 20:47
| Tying in to the main box in existing home Probably 15kw, I'm guessing whether it's 5kw or 25kw, the price physical connection to the box would likely not vary greatly. The size of the generator itself is essentially the same. |
|
- Posted by ronnatalie (My Page) on Wed, Nov 9, 11 at 11:35
| You didn't answer all the questions. |
|
| Unless you get a generator large enough to support the load of everything in the house (and those are very large and very expensive (about 25 kW to 50 kW) only a portion of the house can be backed up. This means that circuits must be moved to a separate panel the generator feeds. |
|
- Posted by ronnatalie (My Page) on Wed, Nov 9, 11 at 16:58
| Actually, that's true only if you are going to use an automatic transfer switch. If you have a manual transfer, then it's allowable that you shed the loads before throwing the transfer switch. I've got an 80KVA with a manual switch. Sort of overkill (I typically only run about 6KVA according to the meter on the generator). |
|
- Posted by growingadvice (My Page) on Wed, Nov 9, 11 at 20:45
| Does the house already stand? Yest as mentioned above. What size generator? As mentioned, not sure. this is part of my research looking into it. I would say in the 14-17kw range. Unlikely it would go over that. Will it serve the whole house? I'm not sure that the kw range I mentioned is enough for the whole house. preliminary research tends to day no Will there be an automatic transfer switch? |
|
- Posted by growingadvice (My Page) on Wed, Nov 9, 11 at 21:05
| meant may not have the choice to go with the automatic switch. |
|
- Posted by petey_racer (My Page) on Thu, Nov 10, 11 at 6:26
| You can go with an automatic transfer panel. One with typically 10-16 circuits. This way you can select the loads you want to switch over and stay within the limits of the generator. Again, without details like what the setting is like, distance from main panel- to transfer panel- to generator, it is hard to say. |
|
- Posted by stinkytiger (My Page) on Thu, Nov 10, 11 at 9:36
| Hi Growing Advice, The question is sort of like how long a piece of string is. However I will give it a bash. All I know about you is that you live in the US and are looking for a Nautral Gas generator set up. I also assume that you are on mains gas, as opposed to propane gas because you mentioned "Natural Gas". I will assume that you will need to have maybe: 1) A new sub panel wired in whith circuts transfered. This panel will house the circuits that are generater backed. I think all in you are looking at $US 3000 to $US 5000 for installation. Generator is extra. A neighbour of mine was quoted $US 14,000 turn key installation for a propane genset, + propane tank + all wiring, permits etc. in New York State. Maybe 14kw sized set. Best, Mike. |
|
| "Actually, that's true only if you are going to use an automatic transfer switch. If you have a manual transfer, then it's allowable that you shed the loads before throwing the transfer switch. " Not a good installation. Someone IS going to screw up the changeover. |
|
- Posted by growingadvice (My Page) on Thu, Nov 10, 11 at 12:18
| I live in western MA. The water line, gas line and electrical line all come in on the other side of the wall where the generator would be. the house was built in 1991, so the wiring is all updated to code. I said natural gas bc believe or not I was trying to be descriptive LOL. There is always a distinction between LP and city gas, which of course is in turn is referred to as "natural gas". Since it involves both gas and electrical, would an HVAC guy install it? around here the ones I've dealt with are licensed electrician and can connect gas lines (at least once in the home, down know about actually piping it from outside. maybe some code thing Or would it be a an electrician and a plumber? If it's much over 1k for installation, then I probably would go with a portable one. We don't loose power that often at all, but with a 2 and 4 year old, it kinda sucked not having power for a week. Dont know if I should start a separate thread, but is there a safe way to attactch a portable generator so the furnace will work, not water heater, stove and the like? thanks for the info. |
|
| Yes, you need an electrician and a plumber. There are two ways to run the furnace with a portable. The first is more costly, you install a manual transfer switch for the whole panel and turn off everything, via the circuit breakers, that you can't power all at once with that generator. Alternatively, you install a manual transfer switch for just the furnace. The latter is going to cost a lot less, but the former will allow you to power other stuff as well. |
|
- Posted by weedmeister (My Page) on Thu, Nov 10, 11 at 14:24
| The third alternative, already mentioned, is to install a subpanel with the furnace on the subpanel. You would then also select circuits like the fridge, freezer, microwave, lights and so on and put them on the subpanel as well. Then during a power outage you use your manual transfer switch to let the generator power that subpanel. |
|
- Posted by growingadvice (My Page) on Thu, Nov 10, 11 at 14:49
| Weedmietser, are you talking with a standby or a portable? |
|
- Posted by stinkytiger (My Page) on Fri, Nov 11, 11 at 7:42
| Hi, It is nice that you have your gas line installed and near your genset site. That can be an expensive item because of trench digging etc. It looks like you can avoid most of that. I am guessing that if you are thinking about a natural gas genset you are looking at maybe a 12-14kw generator set. The way I have my genset hooked up is to have one panel which is the "genset backed" panel. My house has two 200 amp panels. When I installed the genset the electrician moved circuits around so that all the genset-backed circuits was on one panel. That panel is powered with a transfer switch feed. The other panel has circuits that are not getset backed. Looks likeyou have an oil furnace. If you look there is no plug for the oil furnace. This is by code. The oil furnace is wired directly into a panel. So what you need to do is to put those circuits onto the genset panel. So what I would do is: 1) Make sure you have two panels. You may have two panels already in which case that is a "head" start. If not you will have to install another one. 2) One panel will be genset backed one will not. On the getset backed one you will put: the essensials for MA where you live. In approx order of importance: basement sump pump (if you have one) At about 12kw to 15kw that is about the limit for a genset. Air conditioning and electric ovens may be too much usual for a genset of 15kw size so I would not put those on. Hope this give you some idea of what a set up may look like. best, Mike. |
|
- Posted by growingadvice (My Page) on Fri, Nov 11, 11 at 12:34
| Thanks mike. I have a gas furnace. Let me know if that changes anything. |
|
- Posted by stinkytiger (My Page) on Fri, Nov 11, 11 at 15:25
| Hi GrowingAdvice, I think that you have a "gas" furnace probablly does not change things that much. The furnace, oil or gas uses electricity for timer, monitor, controls and most importantly the ignition spark. All these are low power requirements. Well pumps, and forced air blowers, basically anything with a big motor, e.g. Air Conditioning Compressors, they are the things which will use alot of power, or more importantly need alot of surge start current. Best, Mike. |
|
| Where in MA do you live? I am a liscensed, insured electrician and would be happy to give you an estimate and discuss options with you (cost engineering), if you would like. -Chris |
|
| I have a question I am hoping someone could help me out with. I am in the process of having my block converted to natural gas by National Grid on Long Island. I wanted the natural gas for the cost but also the gas fireplace and stove etc. Since Sandy occurred I am also looking into a NG standby generator. When the burner company installs my new boiler I am going to have him add a gas line for a NG BBQ. I was also thinking of having them install the gas line so it would be close to where I would place the generator. I will be renovating the kitchen this summer and was going to have the electrician put in a new box anyway. should I have him install a sub panel and move certain circuts to the subpanel? I would imagine I would want most of the kitchen/laundry room hooked to the subpanle along with few other circuts. any thoughts on this? I am seeing prices of close to $10,000 to install a 14kw generator I could get from home depot for $3,200. at that cost I won;t be getting one. is there anything I could do my self? BTW I would like to think the boiler company would help me out with the plumbing thanks |
|
- Posted by ronnatalie (My Page) on Sun, Dec 16, 12 at 14:16
| $10,000? I installed an 80KVA generator and automatic transfer switch for not much more than that. |
|
- Posted by RockWood13 (My Page) on Mon, Dec 17, 12 at 3:14
| A standby model may cost as little as $1,500 or as much as $15,000 or more--the greater the power capacity, the higher the cost. |
|
- Posted by stinkytiger (My Page) on Mon, Dec 17, 12 at 16:28
| Wow this is a bit of an old thread. But I guess well worth a revisit after Sandy. In New York State, $US 10,000 for a NG Auto Transfer Turn-Key install is about right. About 5 years ago I was quoted $US 14k all in for a 10Kw gen set. Mind you I needed a propane tank installed as well. As a very rough guide, which I did post a while ago I would budget very roughly: 1) Petrol Powered + Transfer switch $US 3,000 to $US 6,000 all in, up to 7Kw Best, Mike. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.