Bathroom wiring questions: # of receptacles; lighting?
| | |
Posted by staceyneil (My Page) on Fri, Nov 6, 09 at 9:53
| (Cross-posted in bathrooms)
We're roughing in the new electrical circuits this weekend. We know that we need either:
1) one dedicated 20A circuit that feeds nothing else but the bathroom
-OR-
2) one 15A circuit for lighting and fan (that can also serve another room) AND one 20A circuit for receptacles that can alos serve another bathroom but nothing else.
We know all receptacles as well as overhead shower lighting must be GFCI protected, and that if we go with option 1 above, at least some overhead lighting should be upstream of the GFCI so it won't go dark if that trips.
Questions:
??????? Do bathroom have the same receptacle requirements as other rooms (i.e. one outlet on each wall, no spot further than 6' from an outlet)?? That would mean 5 outlets in our 13' x 6.5' bathroom! (I do know the sink-spacing requirements for the vanity GFCI.)
??????? Does the recessed light fixture over a soaking tub need to be a waterproof one and GFCI protected, like the one in the shower stall?
Thank you! |
Follow-Up Postings:
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
| Bathrooms are only required to have a single receptacle adjacent to the sink and within 36 inches if the sink edge. Do yourself a favor and run a separate 20 A line that supplies each bathroom required receptacle. Put nothing else on the circuit. A single blow dryer easily hits 15 amps, and sharing between bathrooms will result in tripped breakers. |
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
| If your house falls under the new 2008 NEC, you will be required to dedicate one 20A CB for each bathroom. |
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
| Azlighting wrote "If your house falls under the new 2008 NEC, you will be required to dedicate one 20A CB for each bathroom." Could you post an NEC reference to support this? 210.11(C)(3) and the exception indicate that only one 20 amp circuit is required for all the bathroom receptacles or, using the exception, a 20 amp circuit for each bathroom can supply all the outlets in that bathroom. I can't any wording that requires a dedicated circuit for each bathroom. |
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
| Can you guys clarify that I in fact DON'T need to follow the general receptacle-placement rules in a bathroom (i.e. one on every wall 24" or wider, etc etc etc)? I was planning to put just one receptacle at the vanity and maybe one behind the toilet in case anyone wants to add a washlet later. Should I put any more? Near the soaking tub for a radio or something?? 
|
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
| The only location you are required to have a 20A GFCI protected receptacle under the NEC is between the two vanity bowls as you have it shown above. (You can install 2 separate GFCI recptacles...one on the side walls of each bowl...but the single GFCi receptacle between the 2 bowls meets the Code minimum) You are prohibited by Code to install any receptacles, GFCI protected or otherwise, on the walls within a shower or bath compartment. You are otherwise permitted to install other receptacles in the bathroom anywhere you wish provided they are GFCI protected. "Should you put in more?" I wouldn't.... |
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
| "'Should you put in more?'" "I wouldn't...." Rather short sighted, especially for a bathroom with two sink bowls. A pair of electric tooth brush chargers and that single duplex is full. Unplug one for the blow dryer. Do not forget to plug it back in. Some other electric item? Sorry, you are already out of receptacles. Decide what you have now, what you are likely to need, then wire it now. While it is not that hard to enlarge a box to add more receptacles, it is very inexpensive to add them now. If walls will be tiled it is far easier to do it now. |
RE: Bathroom wiring questions: # of receptacles; lighting?
| | |
Thanks- we were planning to put two duplex receptacles and a light switch on a 3-gang between the vanities, and then a duplex on the wall behind the toilet. As of now, that's it, unless any of you advise otherwise! Many thanks- Stacey and Neil |