Kitchen Remodel (conduit and Wiring)

Posted by mark_anderson_us (My Page) on
Sat, Nov 27, 10 at 7:47

Hi All

I'm about to embark on a kitchen remodel. The house is 1912 and has a lot of knob and tube and old AC with cloth insulation. I'm in Chicago so have to use pipe for everything. I have full access in the basement so will be running a 1" pipe around perimeter. While I have access to the stud bays, I will run EMT from the basement to the 2nd floor to replace existing recepticles and add new ones.

I have a few questions

As I don't have access to the end of any stud walls, running pipe between the studs would be a lot of short sections and connectors, so I figured I'd run vertical emt from the 1" pipe in the basement (lots of junction boxes).

1st question
is this a better method than running lots of short pieces? If I were to run between studs from box to box, would I run conduit at the center height of the boxes (so I come out of right side of one box, through a stud and into the left side of another box).

2nd question
Can I just pigtail the wire to the recepticle in the JB on the floor joist? So I would cut the incoming wire, pigtail the wires for the recepticle (2-4 feet above) and also pigtail the outgoing wires to the next recepticle. Or, do I have to run the wire up to the recepticle, pigtail in its box and then run it back down?

3rd Question
As there will be many circuits in the 1" perimeter conduit, can other circuits pass through a jb where I make a pigtail. For example, the dishwasher and one of the small appliance circuits share the same run for much of the distance, so I would be running the dishwasher circuit through 3 jb's that have vertical runs to outlets above. Is it OK to pigtail the wires for the small appliance recepticles and have the dishwasher circuit pass straight through those JB's

Thanks

Mark


Follow-Up Postings:

 o
RE: Kitchen Remodel (conduit and Wiring)

1. Shorter runs make easier pulls
2. As long as the boxes remain accessible you can do either.
3 How many circuits? You have to watch the conduit fill. You only get 9 #12's in a 1" (and even then it's going to start getting fun to pull. Then remember once you get more than three current carrying wires in a conduit derating comes into play.


 o
RE: Kitchen Remodel (conduit and Wiring)

Answer #1: Probably, given your description of the construction. Neither method is inherently "better" - both have their ups and downs, but if you simply CAN'T run short pieces in between, then that kinda forces your decision anyway.

#2, yes, you're making a junction, which is what junction boxes are for.

#3, yes. The primary consideration is going to be box/conduit fill, but there's no prohibition against multiple circuits in one conduit or box.


 o
RE: Kitchen Remodel (conduit and Wiring)

Ron
I would not pull RHH with outer covering. Is this some Chicago rule that I am unaware of? I would pull THHN and you can use 26 of them in a one inch. I would also probably only use (2) 3/4" EMT and run one around each side, according to how many circuits. I would also run larger circuits like the range or ovens and cooktop seperately.


 o
RE: Kitchen Remodel (conduit and Wiring)2

I would run 3/4" because it is easier and cheaper to find boxes for it.


 o
RE: Kitchen Remodel (conduit and Wiring)

The maximum current carrying conductors in a conduit before you need to derate is 9.


 o
RE: Kitchen Remodel (conduit and Wiring)

"The maximum current carrying conductors in a conduit before you need to derate is 9."

But you also need to keep in mind that the derating for #14 and #12 is NOT 15 and 20 amps respectively.


 o
RE: Kitchen Remodel (conduit and Wiring)

The maximum number of current carrying conductors before you need to derate is three, but that is beside the point. Does anyone here think the op would need one inch conduit to begin with? With only two 3/4" conduits and nine or fewer ccc's in the conduit (so you don't have to increase wire size for 20amp circuits) you could run up to twelve 20amp circuits, which I would think would be more than needed in most kitchens. I have done some pretty large kitchens on eight 20amp circuits. My point is that you don't have to overkill a job on pipe size when it will only cause inconvenience if not problems. I would use combination 1/2" and 3/4" knockout deep boxes and use 1/2" conduit on the stubups to the wall boxes. Just because you are doing it yourself does not mean you need to install overly large conduit. You will still need to increase wire size after 9 ccc's in 1" conduit as well.


 o
RE: Kitchen Remodel (conduit and Wiring)

You derate after 3 conductors. However derating starts a 20amps for #14. Therfore you don't drop below 15 amps until you have over 9 conductors.


 o
RE: Kitchen Remodel (conduit and Wiring)

Hi guys

Thanks so much for all the useful info and advice.

Based on feedback, I think I'll do 3/4" around the perimeter (in basement) and 1/2" for stub ups. Separate conduit for electric oven

One other question:

Can I come out of a JB in basement to several outlets (so for a run of 3 outlets, I'd come out of JB on pigtail, go to 2 middle of runs and then one end of run) and the same on another JB on the same circuit?


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here