My buddy just bought a house and the main 200 amp panel is in his basement. In his detached garage there is another panel that has a 100 amp main breaker. This breaker is fed from the 200 amp main panel but is terminated on the same lugs that the utility/meter service cable are in. Is this ok?


Follow-Up Postings:

 o
RE: electrical question

If the sub-feed is literally under the same lugs as the 200A main cable in the meter pan then NO, IT IS NOT OK!

Your post is contradictory though, you say it is under the same lugs, but you also say it is fed from the 200A panel. Which is it?


 o
RE: electrical question

Not the meter pan but under the 200 amp breaker lugs


 o
RE: electrical question

So the conductors to the 100 amp garage panel are installed at the top of the 200 amp breaker?


 o
RE: electrical question

Yes


 o
RE: electrical question

Not OK for two reasons.

First those lugs aren't designed to have more than one conductor in them. That alone is potentially causing problems.

Second the feeder needs over current protection which is not being provided.


 o
RE: electrical question

Agree about the matter of the lugs and that alone is enough to fail inspection. Another concern is the length of the run to the garage panel that has no on-premises overcurrent protection.


 o
RE: electrical question

It needs to be fed from a 2 pole breaker.


 o
RE: electrical question

Ok I will tell my friend this needs to be fixed. I appreciate it thanks.


 o
RE: electrical question

I would verify if it is fed with a 4 wire or 3 wire feeder. It needs 2 hots, 1 neutral(insulated) and 1 ground.


 o
RE: electrical question

Which also leads one to wonder if the circuits in the subpanel have neutral and ground separated...


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here