Hardwired smoke detectors, interconnect...

Posted by pharkus (My Page) on
Thu, Oct 28, 10 at 23:35

... grrr... sometimes I hate doing work for friends.

I've inherited a project involving... umm... six? yeah, six hardwired smoke detectors.

Wouldn't you know it - only four can be found. We have no idea where the other two went. All the hardware exists - brackets, connectors, etc., but the detectors themselves? GONE. Vanished. Got sucked into a spontaneously-generated wormhole and transported to an alternate dimension.

I told him to go buy six new, matching units.

He came back several days later with two completely different ones. It is his belief that I should be able to use them.

Y'know what? Whatever. I don't care, there's hot and neutral there, I can just leave the interconnect wire disconnected and forget it. His alternate plan is to just use 9V battery powered ones anyway.


and yet I wonder to myself (but don't dare try it without someone else's input), is the 'interconnect' standard? Do different brands/models use the same signalling? Can I mix brands? Will it work? Will the world end? Will it create another wormhole and teleport more matter? I mean, the latter wouldn't necessarily be a bad thing if I could coordinate it with the presence of his very irritating ten-year-old son...


Follow-Up Postings:

 o
RE: Hardwired smoke detectors, interconnect...

The manufacturer's don't want you to mix an match, as they say they can't "guarantee" the units will operate correctly or to their maximum operating efficiency, but if you install all their units you can!

Shouldn't be a big deal unless manufacturer's have completely different connection guidelines, or wattages, voltages, etc.

Def. verify before.


 o
RE: Hardwired smoke detectors, interconnect...

Well, I'm TRYING to verify before. That's why I asked. :)


The other method I have to verify is to simply clip my meter on to the interconnect wire and press the test button. Frankly if the signal voltages are the same I'm going to wire them up and see if they work. I'm just not at the project house for the weekend (taking a much-needed break) and won't be able to do this until Monday.


 o
RE: Hardwired smoke detectors, interconnect...

Hook it up. When it starts going off or the smokes blow up then you can tell him I told to buy six new matching units. I sure there is probably some code either electrical or fire that requires them to be interconnected and the same.


 o
RE: Hardwired smoke detectors, interconnect...

You're asking for trouble in my experience. I have found that sometimes different models from the SAME manuf. That are supposed to work together have troubles. I wouldn't even bother interconnecting them if they aren't the same brand.Tell your buddy why though.

The funny thing is that the prblems never seem to show up until you have been gone from that job for a month or so!


 o
RE: Hardwired smoke detectors, interconnect...

"is the 'interconnect' standard?"

No, and that is the problem.

There is no standard.


 o
RE: Hardwired smoke detectors, interconnect...

well, tell the dummies who made the dangerous tr recs REQUIRED to make a STANDARD.


 o
RE: Hardwired smoke detectors, interconnect...

There is a standard. A number of them actually, they just don't apply to proprietary residential smoke detectors.

There's a 4-wire standard, for 24V-powered smoke detectors with a set of contacts to report to a central controller that smoke is detected.

There is a 3-wire variant, which shares one of the contact terminals with one of the power terminals.

There are newer digital serial standards.

If I want to turn this guy's house into an office building, school, or factory, then there are definitely standards available. Unfortunately, they require him to buy stuff, something he seems very... uhh... well, did I mention I told him to buy a set of matching smoke detectors and he came back with only two, which don't match either the existing units or themselves???


It appears from my searching the internet that Firex (existing) simply connects the 9VDC supply to the interconnect wire to signal, and both of the new ones are Kidde, which is apparently the same company - whose website seems to indicate they are compatible... At this point, I'll believe it when I see it.


Work resumes Monday.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here