| Am remodeling kitchen - Does it make sense (not just minimum code) to put micro and dishwasher on same 20 amp circuit? Micro has small amperage rating. Also, am placing six outlets in a desk work area over ten feet away from counters and plumbing - but in kitchen - do these need to be GFI. If GFI outlet doesnt specify # of outlets downstream, is it safe to assume 5 is ok? Thanks for your help. |
Follow-Up Postings:
|
| dw amd mw need seperste recs. dw needs line of sight disconnect. all counter recs must be gfi protected. use a gfi breaker. i prefer to use 2 duplex/ circut. dont have nec next to me like ontariojer. |
|
| "dw needs line of sight disconnect" not true, you can possibly put a lock off on the breaker, I do it all the time much faster and easier. Check with your AHJ " use a gfi breaker" there is no need, GFCI receptacles are fine. It will add significant more cost to use GFCI breakers |
|
| i have seen a 1970's qo gfi breaker that still works today. i have seen a cooper 15a gfi last 2. we replaced it like 3 times. |
|
| "i have seen a 1970's qo gfi breaker that still works today. i have seen a cooper 15a gfi last 2. we replaced it like 3 times." Do you have any idea what GFCI devices cost? You can use a single GFCI receptacle (~$10) to protect downstream receptacles. Two small appliance branch circuits are then $20 for the GFCI receptacles. I do not recall seeing a GFCI breaker for anything approaching $10. |
|
- Posted by ronnatalie (My Page) on Thu, Oct 21, 10 at 8:11
| All the countertop receptacles need to be GFCI protected, you'll have to check with your local authority as to whether the desk would be considered a countertop by their definition. All the receptacles including the ones on the desk area (with small exception) need to be on two or more 20A circuits shared with (again small exception) NOTHING else. There's no limit on the number of receptacles strung on each circuit or GFCI. I would generally recommend an additional circuit for the dishwasher and the disposer. As long as the receptacle that these are plugged into is accessible (under the sink is the common placement) disconnecting the plug suffices for the disconnect requirement in most places. A small countertop microwave usually isn't a problem. I'd definitely go with a dedicated circuit for the larger units. One thing to do is to check the manual/installation instructions on the various appliances and see what it recommends. If they "REQUIRE" a dedicated circuit, you're obliged to use it. If they recommend it, you should definitely consider highly that recommendations |
|
| a qo gfi breaker costs ~$66. a p&s 20a tr gfi costs ~$13.50. the cb will outlast the gfi. |
|
| "a qo gfi breaker costs ~$66. a p&s 20a tr gfi costs ~$13.50. the cb will outlast the gfi." I'm sick of this... Give facts to back it up or STFU, all your doing is spamming the hell out of this board with your opinion. Going around claiming how QO is the second coming of Christ is getting old. Get some actual field experience instead of just putting in some recp's and switches for your friends. In short, smithy, you really have no idea what you're talking about it. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.