GFCI tester - open ground?

Posted by gene_2007 (My Page) on
Tue, Oct 28, 08 at 20:55

I just installed a new bathroom circuit. It's pretty simple - one receptacle, fan/light, vanity light, two switches. I tested the outlet and both switches - all good. The receptacle is GFCI and the load side feeds the double switch for the light and fan/light. I tested the GFCI using the TEST button. That went well, also.


Then I plugged in my Ideal GFCI tester. Two green lights came on. The problem - when I clicked the test button on the tester, it did not trip the GFCI outlet, and the lights changed, indicating that there is an open ground.


I checked everywhere and can not find an open ground. I also checked for an open ground by using my neon tester between each of the black wires and the ground wire.

Perhaps the GFCI outlet is defective? Is there anything else I can check?


Follow-Up Postings:

 o
RE: GFCI tester - open ground?

How old is the GFI? Are you absolutely certain you got LINE and LOAD correct?

Also, WHY did you protect the lighting?


 o
RE: GFCI tester - open ground?

Everything is brand new.
Line is fed from circuit breaker. Load is to switches.
I protected the lighting because the fan/light is above the shower/tub. I suppose I didn't have to protect the vanity light.


 o
RE: GFCI tester - open ground?

How old is the house and wiring?

A GFCI does not require a ground to operate, and the test button on the device will still work.

A GFCI tester requires a ground to check GFCI operation.

Even if there is a ground in the bathroom wiring, it may not go back to the panel and actually be hooked up.


 o
RE: GFCI tester - open ground?

It is an older house, but new panel. Besides, I ran the new circuit and breaker. It is definitely grounded.


 o
RE: GFCI tester - open ground?

Does the real loads (not the tester) go off when you push the test button (either on the GFCI itself or the tester)? The little neon bulbs in these things can sometimes light just from stray coupled voltage.


 o
RE: GFCI tester - open ground?

When I press the TEST button on the GFCI, it kills the circuit. When I click the button on the tester, it does not - everything stays on and the lights (on the tester) indicate that there is an open ground. I can not find any open ground. What are the chances that the tester or the outlet are defective? Are there any other things that could be wrong that would make my tester fail and indicate an open ground condition?


 o
RE: GFCI tester - open ground?

Does this tester behave properly on another known good receptacle?

Do you have a grounding wire going to the screw on the GFCI receptacle, or are you counting on contact through its mounting yoke (not approved and perhaps not working)?

Can you rig up a light bulb tester connected to the hot (black) and ground (green) of an old power cord and see if that trips the GFCI?


 o
RE: GFCI tester - open ground?

Yes, tester works on other GFCI outlets (in kitchen).
Yes, the line cable's ground wire is connected to the green screw on the GFCI. The two other cables' (the ones going out from the switch to the lights) ground wires are pigtailed and connected to the ground screw on the double switch.
Can you explain in a little more detail the last paragraph. Are you saying plug in an old power cord into the outlet and then check the wires?


 o
RE: GFCI tester - open ground?

If you aren't comfortable with that kind of experimentation, don't try it. The idea was to find a light socket and power cord that could be wired together in a non-standard way in order to do a test here. The light bulb would be connected between hot and ground. Plug it into the GFCI receptacle. If it lights without tripping the GFCI then the GFCI is bad or something isn't wired right. If it trips, then maybe the GFCI just isn't quite as sensitive as most of them are or the push button tester doesn't draw as much leakage as it was intended to so that it takes a more sensitive GFCI to trip. If it doesn't light but the GFCI doesn't trip either, then you don't have a real ground connection through the GFCI receptacle.


 o
RE: GFCI tester - open ground?

Use a volt meter and measure from the hot to the ground of the receptacle.
Then measure from the hot to the neutral.
If the readings do not match the ground is bad (not a perfect test since the current is low, but if the GFCI tester is low also).

If they do match try another GFCI receptacle.

The one you have could be bad internally and not making contact with the ground pin of the tester.


 o
RE: GFCI tester - open ground?

I don't have a light socket handy, so I haven't tried that yet.

I did check the wires with the voltmeter. Both white and ground came back exactly the same - roughly 116 volts.

I noticed that when I press the GFCI test button on the TESTER in any outlet that is NOT GFCI, the lights indicate "open ground." So, I'm thinking that maybe the lights don't really mean anything in this case - the tester is just not recognizing this as a GFCI. As billhart said - "maybe the GFCI just isn't quite as sensitive as most of them are or the push button tester doesn't draw as much leakage as it was intended to so that it takes a more sensitive GFCI to trip."

Should I forget about it and assume everything is okay, or should I try the billhart experiment, or just buy another GFCI outlet and try that?


 o
RE: GFCI tester - open ground?

Or try another GFCI tester.


 o
RE: GFCI tester - open ground?

[Use a volt meter and measure from the hot to the ground of the receptacle.]

In a properly functioning GFCI this will cause the device to trip.


 o
RE: GFCI tester - open ground?

sumac - I'm really glad you mentioned that because that exact question crossed my mind. It seemed logical to me that if I was completing a circuit using the ground wire, then the GFCI should definitely trip.

I bought a new outlet and a new tester this morning. I'll be doing some more testing later on this evening.


 o
RE: GFCI tester - open ground?

In a properly functioning GFCI this will cause the device to trip
A voltmeter will not place enough of a load on the ciruit to trip a GFCI. A solenoid type tester (Wiggy) will.


 o
RE: GFCI tester - open ground?

I switched the GFCI outlet- exactly the same results, so we can rule that out.

I tried the new tester that I bought. This one worked on the GFCI outlet, but not on the outlet downstream! The outlet downstream, by the way, is an outlet that I attached for testing purposes. Later, this will be the vanity light.

I'm getting a little frustrated now. I'm not too proud to say that it sounds even to me like it must be a wiring problem, but there is so little here, I don't know what I could have done wrong.

Here is exactly what I have - this is all new wiring from the panel:
  • 12/2 from panel to GFCI LINE (black, white, & ground to proper screws)
  • LOAD side of outlet

    • White - pigtailed (two loads - vanity light & fan/light)
    • Black - common terminal of double switch (tab still attached)

  • Two ground wires from the vanity and light/fan are pigtailed and attached to ground screw on double switch
  • Two black wires (from vanity and light/fan) are attached to the two screws on the switch

So, to sum up one more time - everything appears to be working fine. The switches properly control the vanity light (I have a regular duplex outlet attached temporarily) as well as the fan/light above the tub. The outlets have power and the testers indicate that they are wired properly. The TEST button on the outlet works fine. The concerns that I have are:

  1. The "old" tester that I have won't trip the outlet; however, it works on all of the other GFCI outlets that I have elsewhere in the house.
  2. The "new" tester trips the GFCI outlet when plugged directly into it; however, it does not trip when I plug it into the outlet downstream (which will later be the vanity light).

Yes, I know that the vanity light does not need to be GFCI protected, but I won't feel comfortable if I don't understand why this isn't working. The shower fan/light is supposed to be GFCI protected, so how will I know if it really is?


BTW - the GFCI outlet is 20Amp and the circuit breaker is 20Amp


 o
RE: GFCI tester - open ground?

I can't tell from your posting.....

""12/2 from panel to GFCI LINE (black, white, & ground to proper screws) ""

""Two ground wires from the vanity and light/fan are pigtailed and attached to ground screw on double switch ""

All these grounding conductors from the GFCI and the switch need to be connected together...Are they ?

At the VanityLightTempRecpt.....check for voltage between Hot and Ground.........


 o
RE: GFCI tester - open ground?

From your text, it sounds as though, when you have multiple devices in the box, you've been attaching the "line" ground wire to one device and all of the "load" ground wires to another.

This is not how it's done. They ALL have to be connected together.

Hopefully I'm misunderstanding you - because, if I'm not, you now have to go back to every single box in your house that has multiple devices in it and fix them all.


 o
RE: GFCI tester - open ground?

The box is metal, so originally, I figured that they would all be connected via the outlet yokes and the box itself. However, to eliminate any question, I did add another wire to tie all of the ground wires together.


 o
open ground? - sensitive?

Is it likely, or possible, that the GFCI outlet is just not sensitive enough? Even though I bought a second one, maybe it's the way they are manufactured. Should I bother trying a differnet brand/model?


 o
Test ground from VanityLightTempRecpt

At the VanityLightTempRecpt.....check for voltage between Hot and Ground.........

Yes, I tested the hot/ground with my voltmeter and got the same reading as I did on the GFCI outlet.


 o
RE: GFCI tester - open ground?

12/2 from panel to GFCI LINE (black, white, & ground to proper screws)

LOAD side of outlet

White - pigtailed (two loads - vanity light & fan/light)

Black - common terminal of double switch (tab still attached)

You need the ground from the load side of the GFCI to attach with the other ground to the line side of the GFCI.


 o
RE: GFCI tester - open ground?

All the grounds get connected together on both sides of a GFCI receptacle.

If you are not hooking the load side grounds to the line side ground in the GFCI box you have dropped the ground.

The GFCI function downstream will operate correctly (it does not need a ground) but the GFCI tester requires a ground to leak current to trip the device.


 o
All good now!

Thanks to you all. You all steered me in the right direction. It was definitely due to the grounds not all being wired together. I was relying on the yokes and the metal box, but apparently that is not sufficient.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here