| Hi,
I am installing a hot tub next week and want to make sure that I have the correct wire and components.
The store I purchased the tub from sold me a 40 amp GFI outdoor spa panel but would like confirmation that this is correct. I was planning on using #6/3 NMWU-90 wire which I think should be more than adequate. Finally I was planning on using a 2 pole 60A breaker in the main panel, I have started to think that this might be a bit big but there is provision in the spa box for two auxiliary 15A circuits that I thought I might use at least 1 of them for some outdoor lighting. Speaking of these auxiliary circuits, I was talking to the guy at Home Depot and he said I should not use them. Anyone have an opinion on that? Thanks in advance for any input you might have. Cheers. Jim |
Follow-Up Postings:
|
- Posted by mike_kaiser (My Page) on Sun, Oct 17, 10 at 20:29
| NMWU-90 Can't use NM, the ground(ing) conductor needs to be insulated. Have you looked at the manufacturer's web site for additional installation information? Sometimes the manuals provided with the spa is has been updated or the manufacturer provides additional information. |
|
- Posted by ontariojer (My Page) on Sun, Oct 17, 10 at 20:43
| I see you are in Canada- Where? If you are doing this yourself to save money: The Hot tub should say on the rating plate what breaker it requires. YOU SHOULD GET A PERMIT AND HAVE THIS INSPECTED. If you want to do it the other way, that is fine too(as long as the spa panel is the appropriate distance/inaccessible from the tub). But if you are willing to spend the extra money, why not have an electrician do the work, then you can relax as the bubbles take your cares away, and not wonder if you are about to be electrocuted because you didn't hook up the GFI properly. Just some food for thought. |
|
- Posted by jrturner92 (My Page) on Sun, Oct 17, 10 at 21:21
| "I see you are in Canada- Where?" Rural MB "If you are doing this yourself to save money:" Mostly to get it done, i am having a hard time getting contractors to show up. "The Hot tub should say on the rating plate what breaker it requires." Maybe, the tub is still on a pallet. "If the HT only requires a 40A breaker, you are spending way more than necc. on that 6/3 wire, 8/3 should do ya(unless the HT is a long way from the house." I will need a bit more than 110 ft of wire to get from the panel to the tub. "Also, as long as the spa panel has a locking cover or a way to lock the breaker(most do), you don't actually have to put it outside." Basement is fully finished so going outside will be easier. "Make sure the NMWU is protected properly, especially make sure it is buried deep enough if you are running it underground." 18" and covered with clean sand. "YOU SHOULD GET A PERMIT AND HAVE THIS INSPECTED." I plan to. |
|
| I would use a 60a gfci in the house and 4 awg thhn in conduit to the line of sight disconnect. I would then use a40 for the tub and a 20 for the service rec. |
|
- Posted by petey_racer (My Page) on Mon, Oct 18, 10 at 6:49
| Smithy, WHY would you waste the money on #4 (!) when it has been determined that #8 will be perfectly adequate??? jrturner92, in the US you CANNOT use NM or UF for the outside portion of the wiring to a hot tub. We MUST use conduit can conductors with an insulated ground. I believe Canada is the same. You guys have something called Tek cable I believe. This is the ONLY flexible cable allowed for the outside portion of the wiring. Also, I see that you do not plan to do this, but I believe Canada is the same in that the disconnect MUST be within sight of the tub. So putting it in the basement, even with a lock, is NOT a consideration. |
|
- Posted by ronnatalie (My Page) on Mon, Oct 18, 10 at 6:53
| Don;t know how things run in Canada, but in the US it's usually cheaper to put a breaker in the panel and then use a "spa pacK' which is a combo GFCI/disconnect box (runs about $90 at the home centers) as the disconnect. |
|
- Posted by ontariojer (My Page) on Mon, Oct 18, 10 at 7:20
| Canadian rules are very different for hot tubs- no need for conduit. NMWU is fine. See my post above about disconnects- they do not have to be line of sight(in residential installations). He does have a spa-pak. Has to have a lockable Disc. here as well, but it can be out of sight. Ignore smithy, I have decided he is a troll. In one post he says he's 14y.o. |
|
- Posted by jrturner92 (My Page) on Mon, Oct 18, 10 at 12:00
| Ok, so it seems on on the right path. Any comments on putting an auxiliary circuit in the GFI box? Thanks |
|
- Posted by ontariojer (My Page) on Mon, Oct 18, 10 at 14:21
| If you feed the spa pak with 60a like you were planning, I don't see any reason you shouldn't use it for something else as well. |
|
| I was modifying the idea i had when my grandparents were considering adding a hottub. i was going to run 100a from the main panel to the pool subpanel. i was then going to run 60 to the disconnect panel and add the service rec and a lighting circut to add a nearby(20 feet away) dusk to dawn lamp. i planned to match the other sqd qo panels on the property. |
|
- Posted by jrturner92 (My Page) on Sun, Oct 24, 10 at 12:56
| Possible stupid question: What is "service rec"? Thanks |
|
| in america, we are required to have a receptacle within 10 feet(or something like that) of the hottub. it must be gfi protected. |
|
- Posted by petey_racer (My Page) on Mon, Oct 25, 10 at 7:04
| "...or something like that...." ???? Seriously? No, it's not "within ten feet". Easy answer. It means Service Receptacle. |
|
- Posted by ronnatalie (My Page) on Mon, Oct 25, 10 at 8:37
| Not less than six feet nor more than ten and it applies ONLY to indoor installations. If you're going to deal with tanks of water that you immerse yourself or your loved ones in, it behooves you to read ALL of art. 680 and understand it rather than relying on your memory. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.