Help needed in Los angeles

Posted by newbie_underfire (My Page) on
Sat, Oct 9, 10 at 19:13

Have someone suing me and they have a newly lisenced GC who claims that having a mian breaker in the sub panel is against code - can anyone tell me if this is true and if not the california code that I can use to say its not


Follow-Up Postings:

 o
RE: Help needed in Los angeles

in NJ I installed a sub panel and it was definitely wrong to have a main breaker in it. The main breaker is the breaker in the main panel that is feeding the subpanel. Its redundant anyway if you think about it. The sub panel had a groung and a nuetral that BOTH go to the main panel ground.


 o
RE: Help needed in Los angeles

I think your first call should be to your local building department. They're the final authority as to what is acceptable and what is not.

Who installed this sub-panel? Was it inspected? If so, that should cover you.


 o
RE: Help needed in Los angeles

Using a load center equiped with a main breaker for a sub-panel is done all the time and there is nothing wrong with it per se. The "main breaker" in the sub-panel becomes nothing more (or less) than a local disconnect for the sub-panel.

My hunch is that either (1) the 'GC' (who, btw, is probably not a qualified expert for the purposes of court testimony on electrical matters) doesn't know what s/he is talking about or (2) the alleged code violation is something other than what you've described.

Off the top of my head, here are a couple of possibilities you might want to consider:

The local sub-panel disconnect (i.e., second "main breaker") does nothing to protect the feeder wires from the main panel to the subpanel. Thus, if you wired the feeders from the main panel lugs (as opposed to a properly sized breaker), the feeders are exposed to the total current of the main service and may be undersized.

For example, assume the house has 200A service and you wired a 100A subpanel using #2AWG wire connected to the main lugs. While #2AWG is adequate for the 100A subpanel, it is not adequate for the 200A supplied to the main lug and this would be a code violation.

What size feeder conducters were used and are they properly protected by a breaker in the main panel? Assuming that they're connected to a breaker, it is THAT breaker that is the important overcurrent device and the primary disconnect for the sub-panel.

Secondly, it's possible that you interpreted the fact that the sub-panel had a "main breaker" and was marked suitable for use as service equipment" as meaning that it should be wired like a main panel -- specifically that the neutrals and grounds can be co-mingled as is legal in a main panel. Does the sub-panel have a ground bar and are the neutrals and equipment grounds kept isolated? If not, then you have a code violation.

Finally, it's possible that the "GC" is the one doing the misinterpreting. That is, perhaps s/he decided (incorrectly) that since it was a "main panel" the neutrals and grounds should be bonded.

Who knows? You need more facts.


 o
RE: Help needed in Los angeles

"in NJ I installed a sub panel and it was definitely wrong to have a main breaker in it."

They must have changed the local code since the NEC does not prohibit a main disconnect in a sub-panel.

It is not required, but does make working tin the box at least a little safer.

You can turn off the 'main' in the panel and know that the breaker lugs are no longer hot.

Only the panel feed and the source side of the 'main' remain hot.


 o
RE: Help needed in Los angeles

A main breaker in a subpanel is POINTLESS unless it is smaller than the feeder breaker. if it is the same size or larger then it decomes a ''line of sight disconnect'' (joke)


 o
RE: Help needed in Los angeles

A larger main breaker in a sub-panel may be pointless, but it is frequently cheaper to use it than a panel without. Like HALF the cost sometimes. Supply and demand I guess. Kind of like spa- paks vs. Tandem GFI breakers.


 o
RE: Help needed in Los angeles

OJ has it right. Often you can get package deals in one carton, with a main panel and several breakers, for less than you'd pay for a main lugs panel alone. I guess it's because they're produced in large quantities for builders and the competition is strong.

A main breaker in a sub is no big deal aye or nay, if the sub is right next to the main panel. But if it's on the other side of the house, or on a different floor, that local disconnect is nice to have.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here