Moved GFCI to panel, trips

Posted by janwad (My Page) on
Sat, Oct 2, 10 at 14:04

I had a garage gfci outlet that controlled the power to all 3 bathroom outlets, and a couple of low voltage 35 watt halogen bulbs in the master bath.

The garage was remodeled and yesterday the electricians moved the GFCI from the garage outlet to the panel. I think they moved the garage outlet to a different circuit.

This morning it tripped after 3 minutes of hair dryer and the 2 lights. That combo never tripped it before. I'm the only one home and nothing else is running except the toothbrush charger.

Do GFCIs on the panel limit the load that much? Would it help to move the GFCI to the first outlet instead?


Follow-Up Postings:

 o
RE: Moved GFCI to panel, trips

Have the electricians do the diagnosis and correction.


 o
RE: Moved GFCI to panel, trips

Hair dryer's are notoriously high loads (as anybody with teenage daughters can attest to). A GFCI doesn't change the load at all unless someone used a smaller GFCI than the breaker that was there before.

You've probably got an older house that had the bathrooms and the outside receptacle all on the same circuit so they could share a GFCI. If this was wired up with 12G wire, confirm that the new GFCI breaker is a 20A one.


 o
RE: Moved GFCI to panel, trips

A GFI doesn't provide ANY overcurrent protection. An overload won't trip it. If it's tripping, it's because it's detecting a potentially hazardous leakage current condition.


 o
RE: Moved GFCI to panel, trips

There is probably an unintentional connection from neutral to ground between where the GFCI was located before and the panel. Now that the protection is back at the panel, the problem connection is being noticed and is causing the trip.


 o
RE: Moved GFCI to panel, trips

if the GFCI was moved "to the panel", I'm assuming it's a GFCI breaker. It WILL provide overcurrent protection, it is a combination device.

I believe the explanation is that a smaller breaker was installed.

Unintentional ground/neutral connections will definitely trip GFCIs, but this should happen a lot quicker than 3 minutes, and shouldn't require much of a load (if any) to occur.


 o
RE: Moved GFCI to panel, trips

Thanks for the responses. I will contact the electrician, and I appreciate having some more info so I can be prepared to understand him better.

You guys are invaluable.


 o
RE: Moved GFCI to panel, trips

"...tripped after 3 minutes of hair dryer and the 2 lights."

That is the breaker tripping on thermal overload (and a few minutes is not a very large overload).

The GFCI function would trip instantly if there was a neutral or other wiring issue unbalancing the hot current and neutral current.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here