240 volt wiring for a spa

Posted by MarkMaurer (My Page) on
Sun, Oct 28, 12 at 13:14

I am needing a 50 amp circuit for my new Jaccuzzi spa. I have read that I need to use 6 guage wire for this. Problem is the length of the run for my yard. Over what length can I run the 6 guage before it is too small of a guage? I had a similar situation with my low voltage lighting in the backyard. I was about 200 ft. total and was told to use heavier guage for the first half of the run. My run for the hot tub will be about 150 l.f.


Follow-Up Postings:

 o
RE: 240 volt wiring for a spa

Number six should be fine for 150' at a nominal 40A load.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here