GFI Problem

diz71266
13 years ago

I recently replaced a GFI for a friend in his kitchen and ran another switched outlet outside from the load side of the GFI.There was existing there another wire on the load side that powered 3 more outlets in this kitchen (they were nowhere near the sink and another one by the sink is NOT hooked into a gfi circuit so I think an earlier installer did something wrong,but this is just for info and I dont believe relevant to my problem)The problem is as soon as I plug something in the outside outlet it trips the GFI.I can plug the same thing in to one of the kitchen outlets that are on the GFI circuit (or the GFI itself)and it works fine but the new outlet outside trips the instant something is plugged in.Did i miswire somehow? I used the backstab holes on the load side (there were 2 sets of holes on both the line and load side)Into one set I put the wire that powered the 3 kitchen outlets and into the other set I put the neutral wire going to the outlet outside and on the hot side I put the black wire which went to the switch and then outside.

Thanks in advance for your input.

Comments (13)

  • Ron Natalie
    13 years ago

    This is why it's illegal for you to do what you're doing.

    If the GFCI trips with a load, it is almost assuredly because one side of the part of the circuit with that load is connected to the protected side of the GFCI while the other is not.

    I have this strange feeling you've connected the neutral to the load side of the GFCI but booted the hot from somewhere else. What switch?

    Depending on where you are and when the house was built, all the countertop outlets should be on a GFCI. I suspect that since the GFCI is also feeding things that are outside the kitchen this is an older house OR some other hack has already introduced code violations.

  • diz71266
    Original Author
    13 years ago

    from the exterior receptacle>> The black wire goes to a switch and then to the LOAD side HOT terminal of the GFI
    The white wire goes to the LOAD side NEUTRAL terminal of the GFI...is there any reason this setup should not work?

  • brickeyee
    13 years ago

    Even if you can get it to work, you are not allowed to feed an outside receptacle from the kitchen counter small appliance branch circuits.

  • Ron Natalie
    13 years ago

    Well, there's also the possibility that there's a ground fault somewhere else.

  • brickeyee
    13 years ago

    I would abstain from providing advice for an illegal installation.

  • diz71266
    Original Author
    13 years ago

    This sounds like one of those situations where a code is written just to pump more money into the hands of electricians..to tear apart a house from one side to the other to install a dedicated circuit for an exterior receptacle is ridiculous..Unless you can explain to me the safety issue with it.

  • brickeyee
    13 years ago

    "This sounds like one of those situations where a code is written just to pump more money into the hands of electricians..to tear apart a house from one side to the other to install a dedicated circuit for an exterior receptacle is ridiculous..Unless you can explain to me the safety issue with it."

    You do not need "to tear apart a house from one side to the other to install a dedicated circuit" if you now what you are doing.

    The safety issue is that the kitchen counter circuits are 20 amp small appliance branch circuits, are sharing them with other loads can result in overloads.

    The 'safety issue' is also that the NEC when adopted by jurisdictions normally has the force of law.

    Luckily your homeowner's insurance does cover your own mistakes.

  • Ron Natalie
    13 years ago

    Unluckily his homeowner's insurance won't cover the mistakes he's making to his friend's house he's "helping."

  • ontariojer
    13 years ago

    You are very welcome for the free, experienced advice. Have a great day.

    Signed,
    Your local electrician.

  • petey_racer
    13 years ago

    "This sounds like one of those situations where a code is written just to pump more money into the hands of electricians..to tear apart a house from one side to the other to install a dedicated circuit for an exterior receptacle is ridiculous."

    What an absolutely moronic statement.

  • smithy123
    13 years ago

    "This sounds like one of those situations where a code is written just to pump more money into the hands of electricians..to tear apart a house from one side to the other to install a dedicated circuit for an exterior receptacle is ridiculous."

    true. you cannot be doing something outside and doing something inside at the same time. at least it is not as bad as what the last people did to my house. they ran 12/2g to my back porch light from the counter recs. then, they ran 14/2g for a loop switch. i had to terminate the 12/2 in the light box and then use the 14/2g to powerfeed the light. the wire in the switch box was also 14awg on a 20a cb, so i had to downgrade the breaker size in my terrible ge panel.

  • Ron Natalie
    13 years ago

    Smitty, Please do not espouse this illegal and unsafe nonsense. Even after your alleged "downgrade" you're still got an illegal installation.

    As far as the OP, you're allowed to DIY your self and your family to death on a single family home but that doesn't extend to others. The truth of the matter is the GFCI may have been indeed grandfathered as it was previously hooked up and it was probably hooked up right, but somehow in your screwing around, you've introduced a ground fault that now needs repairing and we can't do it over the internet. You'll have to have your friend suck it up and call an electrician to fix your mistake.

  • norman1964
    9 years ago

    Serious? NEVER wire kitchen circuit to anything else.....it consumes enough via the toster oven and coffee maker. (1) What you are doing is WRONG, before you even address the tripping problem.
    (2) NEVER backstab. Use the screws. Screws already used?...then it's time to pigtail. Not enough room in the box...yet, another reason not to be doing what you are doing.

    In Ithaca, they would shut down your friends electrical service until you get reinspected, if you mention what you have done, and the failure to get a gfi, and a simple switch to work together. SHUT DOWN...for about two days....