I would love to run some electric back to this cabin that would run the following - mini fridge 1.2 amps,
Here is the balance of the electrical items that we use. 2.5 gal. hot water heater 12.5 amps
Our water system is feed by a 12 volt pump. I do own a Kubota with back hoe so I can dig the trench for direct burial cable. What size wiring would I need to accomplish this. I am open to any and all ideas. Thanks,
|
Follow-Up Postings:
|
| What exactly do you consider "an outrageous amount"? You may find that it is quite reasonable when you start comparing it to 1500+ ft of 500mcl Quadplex. |
|
- Posted by buckeyewilly (My Page) on Thu, Oct 29, 09 at 16:46
| I believe their cost was $12000. |
|
- Posted by spencer_electrician (My Page) on Thu, Oct 29, 09 at 19:42
| If 2/0 aluminum would cut it, the wire would run about $6,000. Then it is all you, trenching/ installation. |
|
| 1500ft of 2/0 AL would drop about 8 volts at 20A. You could watch the lights and know when your water heater was up to temperature. |
|
- Posted by buckeyewilly (My Page) on Fri, Oct 30, 09 at 9:19
| I think my post might have been misleading. I am only interested in supplying enough power to cover the fridge, lighting & tv which is about 6 amps. The balance of the appliances we would continue to use the generator as needed. Just having the fridge and lights would be great!! |
|
| Using a voltage drop calculator and 30 amps as a reference you need to use 350 MCM. |
|
| Even at a 20A load, you need 4/0, and that's if you run a 120/240 feeder for a subpanel. |
|
- Posted by rjoh878646 (My Page) on Fri, Oct 30, 09 at 11:54
| If i was you, I would invest in a solar panel system with batteries. It would probably be cheaper than running wire. |
|
- Posted by bus_driver (My Page) on Fri, Oct 30, 09 at 17:12
| If it was mine, I might consider using step-up transformer at the source and step-down at the point of use. THWN is rated at 600 volts- requires conduit. Impractical for your distance. Type UF-B cable is typically rated at 600 volts. But you will spend $6000 or more on the cheapest setup I can envision. Without the step-up, use of 120/240 will cut voltage losses to 1/4 that of 120 volt supply for the same amperage if the loads on the 120/240 are evenly divided between the poles. Cable for the 120/240 costs considerably more, but use of smaller size may be possible. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.