| My DH is a simple project kind of guy, so when we wanted to change out our old outlets in the bedrooms we thought it would be simple enough. Each bedroom "had" a switchable outlet due to no overhead lighting and he just rewired the new outlet the same as the old one.
I never really noticed but months after he changed them I went to plug in a lamp and it no longer worked by turning on the switch. After reading many, many post on here I now realise that he didn't remove the tab between the outlet. I would like to be sure that when he goes back and removes this tab he gets the correct outlet. Is there a way to tell for sure which outlet once worked by the switch? Or does it really matter as long as it's on the same line? Thanks for all your help on here Cindy |
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Tue, Oct 13, 09 at 11:45
| It's going to be difficult. The receptacle that needs the tab removed is going to have two wires going to the bronze screw side of it. However, some builders may have also used the receptacle for feeding through to other receptacles which would also have multiple wires going to that side (though a giveaway *might* be only one white wire going to the receptacle). Your guess of the "tab" problem is correct if the light is on all the time now (no matter where the switch is). If the light dosen't come on, then it's something else. |
|
| The receptacle in question will likely have either a red and black wire connected to the receptacle or a white wire connected to a black wire in the box. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.