Tue, Oct 6, 09 at 10:04
| I need to move old BX cable for a switch and outlet in a closet that's going from single door to double doors. Walls are the old pre-drywall 7/8 thick 2-part concrete-like stuff (early 1900's house).
The BX will be a bit too short for the new location, so I would like to use romex, but wondering about how to connect/ground the downstream BX to the closet light if I use a portion of romex? One option, if acceptable, is that I could install a metal junction box high on the the inner closet for both ends of the BX to pass through, and run the romex portion for the switch (and connecting the ground wire to the box). Is this doable? Thanks.
|
Follow-Up Postings:
|
- Posted by mike_kaiser (My Page) on Tue, Oct 6, 09 at 11:09
| All splices MUST be done in an accessible, approved box. You can't use what's sometimes called a "flying splice" where the two cables are attached and left to hang in the wall. In your case you'd bring the old BX into a metal junction box using the appropriate clamp. If there is a bonding strip in the cable, then that gets folded back under the clamp. If not, just use the clamp. Then you'd bring the NM-B (Romex) into the box, again with the appropriate clamp (which will be different than the one you used for the BX). The bare ground wire from the Romex gets attached to the box with a screw. Then make up your hot and neutral connections with wire nuts. |
|
| Thank you. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.