| I would like to drop a deep well pump into my lake to supply water for the yard and garden. I have a Deep Well 4" dia. Goulds pump 3/4 horse 230V Two wire 1 Phase. It will be about 200' from the Breaker Box. I am guessing 10/2 wire, 30 amp Breaker? How do you Wire up a Two wire pump to for 230V? Thanks |
Follow-Up Postings:
|
- Posted by bus_driver (My Page) on Sat, Oct 8, 11 at 9:21
| Just a pressure switch in the line. But protecting those conductors from damage will be a challenge in the scenario you describe. And protecting the pump from in-taking debris-laden water will be another challenge. |
|
| It's a 4" diameter about 4' long with built in strainer for Deep wells. I don't think Debris will be a problem since the lake is deep, I can suspend it in about 10' of water. I was mainly concerned about only two wires. Does it need a Neutral/Ground or just the two wires from the 30 amp Breaker? I can do the pressure switch, just connect to one of the two wires? Thanks |
|
| Two hots and a ground. No neutral if the motor is a 240 V load. Cable does not count ground, so it will be labeled 14/2 with ground. Cordage DOES count the ground conductor. |
|
| "Does it need a Neutral/Ground or just the two wires from the 30 amp Breaker? I can do the pressure switch, just connect to one of the two wires?" Your two wire pump has two hots and both must be broken by the pressure switch or whatever control you use, i.e. timer, relay etc. Some areas now enforce three wire pumps & grounding requirements in well service. I am not familiar with code in your usage. Used to be water and steel well casing were considered ground. Your service supply obviously should conform to code whether buried or overhead. Don't guess at conductor size and voltage drop. Determine the pump load at that distance and select ampacity within that range. Size the breaker to the load. IOW, hypothetically you could have #6 wire protected by a 15A breaker. Consider running three wire w/g in the event you want 120V at the line/load connection.
|
|
| "both must be broken by the pressure switch or whatever control you use, i.e. timer, relay etc. " No, breaking one will shut the pump off. A service disconnect must open both hots, but there is no real reason to open both in pump control circuits. |
|
- Posted by bus_driver (My Page) on Sun, Oct 9, 11 at 13:28
| Based on my experience plus the fact that most of those pumps have a Service Factor of 1.5, the #10 wire will be fine for your installation. |
|
| "No, breaking one will shut the pump off." That's true. The OP asks about the pressure switch, which breaks both legs. |
|
| "The OP asks about the pressure switch, which breaks both legs." Save some money and use a single pole switch with a higher quality contact. Any number of thew A/C condenser manufacturers have gone this route. No more crappy contactor with copper contacts, but an actual single high quality relay contact. There is no reason to open both lines in a straight 240 V circuit. |
|
- Posted by ronnatalie (My Page) on Tue, Oct 11, 11 at 13:23
| A pressure switch is not a reasonable disconnect no matter how many legs it switches. He'll need both. |
|
| "A pressure switch is not a reasonable disconnect no matter how many legs it switches. " Yep, and no reason to have the expense of two contacts. |
|
| Again, correct. The purpose of the pressure switch is pump control, not line isolation. Since differential pressure controllers for sub. pumps are double pole, the OP should hook his two line wires to the marked terminals and the load (2 wire pump) on the other side. Personally, I've never had a problem with contact quality, and SP vs. DP are the same price. Ronnatalie, I can show you lots of pump installations with no service disconnect, only line breaker a couple hundred feet away in the basement or in the barn. Sometimes frugality isn't the best choice. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.