| We just bought a new wall oven from Sears (Kenmore). The house has 8-3 wiring (it's a new addition and not previously used).
The oven tag states 120/240V 6.8Kw and in the manual this calls out 30 amps. However when I look at the wires for the pigtail coming from the oven, it clearly says 12 AWG on the wire. I thought 12 AWG is a 20 amp wire. What am I missing and can I connect this to the 8-3 wiring already set up in the house? Breaker size? Also the 8-3 was boxed in the wall with about 6 inches of wire. The oven is a corner unit and I will need to make the last connection to the oven to install or at a minimum and extention from the 6 inces at the wall 2-3 feet to the back of the cabinet. Any ideas my expert friends out there?
|
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Sat, Oct 22, 11 at 9:18
| Do not fret over the size of the fixture wires. Make sure the 8-3 is fed with a 30A breaker (it probably is currently at 40, but the instructions rule here). If I understand you, the 8-3 comes out of a box somewhere that's not possible to connect the pigtail, you'll have to leave the first box accessible and run more 8-3 (or possibly 10-3 but I wouldn't recommend that) wire to a box (probably behind where the oven goes). |
|
| "However when I look at the wires for the pigtail coming from the oven, it clearly says 12 AWG on the wire." The wire sizes you are citing are for general purpose branch circuits, and are held low to provide extra margin in those circuits. There actual load is tightly controlled to just the oven itself. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.