grounding subpanel
| | |
Posted by alfaman (My Page) on Tue, Oct 27, 09 at 0:39
hi.
have an GE DEH-40537 that i am installing in my garage
my question is in regard to grounding...i am confused on whether to use the seperate equipment grounding bus bar or
remove the neutral cross bar and ground on one side there
i know that a subpanel needs to have the neutral and grounds seperate, but wouldn't they be seperate anyway if i just grounded to the seperate equipment ground?...if so...would i have to remove the neutral cross bar if i'm not putting ground wires on it?
thanks..have run an insulated ground back to the main and have driven a ground rod for the sub (in seperate building)
last question is on whether to where to use the bonding screw that came with the box
|
Follow-Up Postings:
RE: grounding subpanel
| | |
| You are right, you don't want the neutral and the case/equipment ground connected in this panel. This panel can be configured either of two ways to accomplish this. You can either remove the bonding screw, leave the cross tie in and use the two bars along side of the breakers are your neutrals while using the one screwed to the case side for ground -OR- Remove the cross tie, install the bonding screw, and use the neutral on one of the bars and ground on the other. Frankly, I think the first option is cleaner. I like having the neutrals landed close to where the hots are. |
RE: grounding subpanel
| | |
| thanks for the reply...appreciate it! |
RE: grounding subpanel
| | |
| Anybody ever heard of a plastic cross tie to replace the metal one some choose to remove to separate the left and right side bars. I hadn't until I got my hand smacked by my local Siemens rep for not using one when doing just that. Yes, they do exist, & he tells me they are "required" any time that tie bar is removed. Who knew? I didn't. So I used one........once. I actually prefer to use the ground bar screwed to the back of the panel tub. When removing the tie bar, it seems like the next guy pays no attention to which side is the ground and which is the neutral. Then you've got a mess. Just my $.02. |
RE: grounding subpanel
| | |
| "...they are "required" any time that tie bar is removed." Sounds like a good reason to add a new ground bar rather than bothering to disconnect the two provided bars from each other. I like having neutral bars on each side. It allows landing the neutral for each branch circuit near the breaker for the hot. If space is available I land the grounds nearby in main panels also. |
RE: grounding subpanel
| | |
| yes...this is why i was a bit confused so my panel has an independent ground bar allready... (this box is sold as a subpanel, so it looks like GE separated the ground bus from the neutral)..ground bar is off to the side so i will not remove the neutral tie bar in this case since the neutral bar and ground bar are allready seperated (as i understands this) |
RE: grounding subpanel
| | |
Correct do not remove the tie bar. Remove the bonding screw. This panel as I said originally can be configured in a number of ways. For your situation leave the neutral bars tied and as the neutral bars. Put the grounds on the other. The other application for this panel is an isolated ground system. In that case you can split the neutral bars and use one as an isolated ground. You don't much see this done outside of certain sensitive electronic and medical applications, you need specialized receptacles, etc... to maintain the isolation. |
RE: grounding subpanel
| | |
| Thanks I see a green boding screw in a seperate plastic package and no ground screw on/in the neutral buss so i guess i simply do not use this screw i plan to put a surge protector in the main panel, so hopefully I won't have a problem with electronics |
RE: grounding subpanel
| | |
| Yep, throw the screw away. |