Armoured Cable

Posted by leslie_gardener (My Page) on
Mon, Sep 12, 11 at 18:48

I'm connecting a short length armoured cable to NM cable in a junction box.
In my reading I see that I have to wrap the bare wire, bonding wire, in the AC around the armour and not to attach it to the ground screw in the box.
I'm puzzled...what is the disadvantage to grounding it to the box?...seems to be the same to me, metal to metal to metal...for my education, what's the difference please?


Follow-Up Postings:

 o
RE: Armoured Cable

You do not have to wrap the bonding wre around at all.

You can just cut off flush before installing the required anti-short bushing (for type AC).

They anti short bushings are usually the little red split sleeves.

They go between the wires and the armor.

Be sure to use the correct cable clamps for type AC.

NM clamps are NOT correct.

The bonding conductor is only there to ensure a continuous ground from the armor (the grounding conductor for type AC cable).

Only one wire can be under a screw head, and you will need to use the hole in the box for the NM grounding conductor.

You must use a metal box with type AC.


 o
RE: Armoured Cable

Brickeyee,

I was under the impression that with AC the bonding strip was folded back along the armored jacket and essentially "captured" by the clamp, not cut flush at the end of the jacket.

Leslie,

Early on armored jacket of functioned as the grounding conductor but over the years they've determined that the ability of the jacket alone to function as the grounding conductor was insufficient so they added a small strip of aluminum to augment the current carrying capacity of the jacket. The rules say that the bonding conductor is not to enter the box.

I'm sure that Brickeyee will chime in here but I'm, too, curious what would happen in a fault if the bonding conductor was tied to the box.

Brickeyee is correct in that NM (aka Romex) clamps look very much like AC clamps but they are not interchangeable. Make sure you use the correct clamps.


 o
RE: Armoured Cable

Mike:

It is NOT necessary to do anything with the bonding strip. It's OK, to do what you want, but what brick suggests is perfoectly acceptable. This explanatory text is in the NEC handbook:


The armor of Type AC cable is recognized as an equipment grounding conductor by 250.118, and the internal bonding strip required by 320.100 can simply be cut off at the termination of the armored cable, or it can be bent back on the armor. It is not necessary to connect it to an equipment grounding terminal. It reduces the inductive reactance of the spiral armor and increases the armor's effectiveness as an equipment ground. Many installers use this strip to help prevent the insulating (anti-short) bushing required by 320.40 (the "red head") from falling out during rough wiring.


 o
RE: Armoured Cable

Thanks for the replies but my question hasn't been answered.
NEC says,"It is not necessary" to connect it to an equipment grounding terminal
"not necessary" translates to "do it if you want to"
But from what I read the text was emphatic in saying "NOT" to connect it to the grounding terminal.
Along with mike i'm curious as to what would happen in a fault if the conductor was attached to the box.


 o
RE: Armoured Cable

""not necessary" translates to "do it if you want to" "

It is a waste of time, and yuo can only have a single wire under a screw head.

It is also not going to mix well in a wire nut since it is small and aluminum.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here