wiring into home grounded?

Posted by ready2moves (My Page) on
Mon, Sep 16, 13 at 17:04

A friend of mine is interested in buying an older home, but the wiring in part of the house has the outlets with the grounding (meaning 3 plug) and part of the house does not have this, just outlets for 2-prong plugs.
Without hiring an electrician, can someone explain to me why the difference in the outlets?
Logically, you would thing the entire house would have outlets with 3-prongs.
any help for them???
thanks


Follow-Up Postings:

 o
RE: wiring into home grounded?

The third (ground) pin is a dedicated conductor back to the grounding electrode system. It is there to provide a low impedence path back to ground (one leg of the receptacle is already grounded, but it carries current and can be displaced in potential from the actual ground).

There are two ways to "fix" a two way circuit. Either replace the wiring such that it adds the third grounded wire ***OR*** protect the circuit with a GFCI.


 o
RE: wiring into home grounded?

The house was certainly built when grounded outlets were not required, or maybe, not available. The owners added some grounded outlets when they needed more outlets (New work must meet current building codes.) or needed a grounded outlet. There is no real reason to have a grounded outlet to plug in devices with only two prong plugs so you can do things piecemeal, when you need them

If you want to plug in stuff with three prong plugs, you need new cable back to the circuit breaker or fuse. Adding GFCI, without ground, might be a good idea where those are now required, wet areas. A GFCI does not provide a proper ground for things that need it and these things have three-prong plugs on them.


 o
RE: wiring into home grounded?

Guess I need to clarify:
original house built with 3-prong outlets in washroom, bathrooms, and kitchen and utility, but the rest of the house has only outlets with 2-prongs.
What possible buyers are wondering is if the electrical needs to be updated which is an additional expense. The original owners of the house now, have lamps, etc all plugged in the 2-prong only rooms just fine.
I am not sure they would need to update the wiring, since where 3-prong is needed, it was there originally.
clearer?


 o
RE: wiring into home grounded?

How old is the house? There is another possibility going on... In the past, you could use armored BX metal jackets as the equipment ground. Do you know if that is being used?

These days, you wouldn't do that. The steel in the BX isn't the best conductor and all you need is one break in the box-to-box connections and you lose the equipment ground.


 o
RE: wiring into home grounded?

To answer the question, do they NEED to have it upgraded? No, I don't think so. If he wants, he can get a licensed electrician in addition to the home inspector to examine the house. Depending on the age, there may be other risk factors that would impact the purchase price (ie, like knob & tube connectors or decayed insulation). Are there circuit breakers or screw-in fuses?


 o
RE: wiring into home grounded?

It is quite possible that the rest of the junction boxes with the outlets in them have grounds run to them. That would be good to know so when it comes time to do the inspection, go with your friend and take off all the covers to look.


 o
RE: wiring into home grounded?

If you want to plug in stuff with three prong plugs, you need new cable back to the circuit breaker or fuse. Adding GFCI, without ground, might be a good idea where those are now required, wet areas. A GFCI does not provide a proper ground for things that need it and these things have three-prong plugs on them.

First off, "wet areas" doesn't really define the areas needed to be protected by GFCI.

A GFCI doesn't provide a ground, but it will protect the operator from fault currents that would have been carried off through the ground if it were present and hence is a LEGAL and SAFE way to use three prong devices. About the only thing that loses in this regard are certain surge protector device that really wanted to sink current to ground.

If you do this there's a requirement to mark the receptacles as not having an equipment ground.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here