Size wire for 125 amp breaker?

Posted by unioncreek (My Page) on
Mon, Sep 28, 09 at 15:38

I own a commercial building that we're turning into a restaurant that has two apartments above it. We've updated the electrical to international fire code, but I still need to run the wiring from the meters to the breaker box. The run will be about 100 feet and the breaker boxes are 125 amp. I'm looking for suggestions on wire size, this is what was given to me by a friend of mine. All wiring will be copper two #2 THHN for hot, one #3 THHN for neutral and one #4THHN for the ground. Do these sound right, I've looked at some of the online calculators and they all say to run #3 for everything.

Thanks,
Bob


Follow-Up Postings:

 o
RE: Size wire for 125 amp breaker?

What does your electrician say?


 o
RE: Size wire for 125 amp breaker?

Bob,

I hope you know that just about every (if not all) municipality prohibits unlicensed people from doing electrical work in commercial establishments and/or multifamily dwellings. The logic is (I think) is you can burn down your own home or kill your own family but not put others at risk.

Good luck.


 o
RE: Size wire for 125 amp breaker?

Tell your friend to keep his day job. I will assume since this is commercial, it is a 120/208V., 3-phase system, but will keep in mind since there is a restaurant it might be 277/480V., 3-phase system.

#2s are only good for 95A without ambient exposure(interior run)and 77A with ambient exposure(exterior run). The 125A MCB will NOT flip if there is a load higher than 95A and you will have a grave situation on hand.

The MINIMUM this needs to be is (4)#1/0's Cu.(three hots, 1 neutr), (1)#6 cu. e.g.(ground) in 1-1/2" conduit for interior run, and (4)#2/0's cu., (1)#6 cu. e.g. in 1-1/2" conduit for an exterior run.

This of course is for a 125A MCB board. If you were to use a 100A MCB board, the copper wires would be smaller.


 o
RE: Size wire for 125 amp breaker?

From his post it sounds like the 125A breaker is the main on the subpanel NOT the OCD for the feeder. Hence, it's a gigantic leap of assumptions to make any recommendation on feeder sizes with this limited information. WIthout knowing what the loads are, the distances involve, etc... it's impossible for even an electrician to answer this question.


 o
RE: Size wire for 125 amp breaker?

azlighting, You are also assuming a lot.
#2 conductors rated at 60 deg C are rated for 95a. Almost nothing anymore is rated 60 deg C, unless you are using old wire.
And, so what if the breaker will not trip at 95A??? We round this UP to 100A since there is no such thing as a 95a breaker.

Also, maybe in AZ you have to regularly adjust for ambient temps, but MOST Of the rest of the country this is not that much of an issue.

Also also, Ron is right, just because the panels are 125a does NOT mean they need to have a feeder rated at 125A. As long as the conductors are rated for the size of the service disconnect OCP.


 o
RE: Size wire for 125 amp breaker?

...but I still need to run the wiring from the meters to the breaker box.

I'd be inclined to think that Bob is installing panels to serve those two apartments.


 o
RE: Size wire for 125 amp breaker?

I'm not assuming anything. Title of the post is "Size wire for 125A breaker", to which I gave an answer.

Where did you get a 95A breaker from, or even a 100A breaker? OP is not asking about those, did you read the title of the post?


 o
RE: Size wire for 125 amp breaker?

The OP does not know what he needs. He is asking for the size wire for a "125a box".

By assuming I meant you are assuming 60 deg C conductors (HIGHLY unlikely), and extremely high ambient temps (quite unlikely).

You make it sound like if the current exceeds 95A the place will burn down.
Read the last sentence of my post. If I am wrong fine, I'll admit that.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here