Wall Mount Hair Dryer

Posted by roger_p (My Page) on
Sun, Sep 1, 13 at 12:42

I am looking for a wall mount hair dryer with integrated GFCI and would like to hard wire without plugging in to an outlet and not break any codes :) Would appreciate some recommendations on the make/model and instructions to hard wire.

Thanks.

Roger


Follow-Up Postings:

 o
RE: Wall Mount Hair Dryer

Just go on Amazon and search hard wired hair dryer. You'll find a number of them, and you can read the ratings.


 o
RE: Wall Mount Hair Dryer

Kudzu9 -

Thanks, but I have done the obvious research. I would like some recommendations from folks who may have gone through something similar.

My questions are:

1. Which hair dryers are the ones with integrated GFCI?
2. How do I wire them(can I draw from an existing GFCI outlet in the bathroo)
3. Specific recommendations

Ideally looking for something compact with retractable wire


 o
RE: Wall Mount Hair Dryer

If you find the hair dryer I am sure that folks here can tell you how it needs to be connected. If you are able to find one that does not use a plug, you will be required to have a disconnect (switch) in the same room.


 o
RE: Wall Mount Hair Dryer

Well not quite. First off, the rule on disconnects is *NOT* "in the same room" but rather "within sight of the appliance." Second, the unit switch can be the disconnecting means in many cases as long as there's an additional disconnecting means elsewhere (which can be a circuit breaker).


 o
RE: Wall Mount Hair Dryer

Interesting, ronatalie. To clarify, a device with a main switch on the device can be hard wired (assuming that it is designed for that)? Are devices with several switches, think electric range, allowed to count this as the disconnecting means?


 o
RE: Wall Mount Hair Dryer

Most definitely if they disconnect all the ungrounded connections (i.e., the hots).

Article 422.34

A unit switch(es) with a marked-off position that is a part of an appliance and disconnects all ungrounded conductors shall be permitted as the disconnecting means required by this article where other means for disconnection are provided in occupancies specified in 422.34(A) through (D).
(A) Multifamily Dwellings. In multifamily dwellings, the other disconnecting means shall be within the dwelling unit, or on the same floor as the dwelling unit in which the appliance is installed, and shall be permitted to control lamps and other appliances.
(B) Two-Family Dwellings. In two-family dwellings, the other disconnecting means shall be permitted either inside or outside of the dwelling unit in which the appliance is installed. In this case, an individual switch or circuit breaker for the dwelling unit shall be permitted and shall also be permitted to control lamps and other appliances.
(C) One-Family Dwellings. In one-family dwellings, the service disconnecting means shall be permitted to be the other disconnecting means.
(D) Other Occupancies. In other occupancies, the branch-circuit switch or circuit breaker, where readily accessible for servicing of the appliance, shall be permitted as the other disconnecting means.


 o
RE: Wall Mount Hair Dryer

If it were me, I'd buy a good quality, plug-in hair dryer and be done with it. You can plug it in wherever in the house you want, you don't have to be worried about how to be code compliant, and you don't have to re-wire anything when it fails. If you want it to stow away like a hard wired one, there are plenty of wall mount dryers available.


 o
RE: Wall Mount Hair Dryer

Thanks, ronatalie, that is all of great interest to me.


 o
RE: Wall Mount Hair Dryer

I have ended up ordering this unit and you will notice it has an in built afci and I can disconnect from the unit.

If I follow the thread by ronnatilie, this would not need a disconnect switch? The disconnect would be the circuit breaker

http://www.sunbeamhospitality.com/product.aspx?pid=11696

Thanks.


 o
RE: Wall Mount Hair Dryer

Make sure you ordered the -040 model as it comes both hardwired and cordless. By the way, it has NEITHER an AFCI or GFCI in it. It has an ALCI which for practical purposes of a builtin unit meets the GFCI requirement (it lacks the ground-to-neutrla fault detection of a GFCI).

The ALCI switch in the base meets the disconnect requirement (provided you've got the breaker elsewhere as described in the NEC excerpt above).


 o
RE: Wall Mount Hair Dryer

I have ended up ordering this unit and you will notice it has an in built afci and I can disconnect from the unit.

If I follow the thread by ronnatilie, this would not need a disconnect switch? The disconnect would be the circuit breaker

http://www.sunbeamhospitality.com/product.aspx?pid=11696

Thanks.


 o
RE: Wall Mount Hair Dryer

ronnatalie thank you! I will give this a shot and maybe post after I hook this up

ionized - thanks

Kudzu9 - good suggestion, but don't want any wires hanging out.


 o
RE: Wall Mount Hair Dryer

Once again, it does not have an AFCI, nor would one be particularly useful.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here