junction box blocked by vanity cabinet

Posted by varnc48 (My Page) on
Wed, Aug 4, 10 at 21:45

I am currently having my bathroom remodeled. Upon inspecting my newly installed vanity cabinet, I noticed that a junction box is 2/3 covered by the cabinet. One of the workmen cut a one inch wide strip from a plastic cover plate, and affixed it somehow over the left hand third of the junction box that extends from behind the new cabinet. When I look inside the cabinet (which has no back), I can see about 1/2 inch of the junction box opening and wires inside. The majority of the box is covered by the side of the vanity cabinet which is attached to the wall. The workmen told me this arrangement is just fine....but my reseach has revealed a junction box should be "accessible." The one in my bathroom does not seem very accessible to me.....Someone please advise, with code reference, if possible...so I can address this with the contractor. I live in California. Thank you!!


Follow-Up Postings:

 o
RE: junction box blocked by vanity cabinet

The code (314.29) says that J boxes must be accessible without removing part of the building. I don't know if cabinets constitute part of the building. It's also supposed to have its own cover. Your "workman" is a cheeseball, IMO. I can't imaging that you like the way this looks and I would have him fix it. If you are having a proper inspection, I doubt it would pass and that would be the final word.
I'm just a DIYer so keep listening to others. Good luck.


 o
RE: junction box blocked by vanity cabinet

The exposed wires will definitely not pass inspection. Move the box either all the way in or all the way out of the cabinet.


 o
RE: junction box blocked by vanity cabinet

"The code (314.29) says that J boxes must be accessible without removing part of the building."

This is not what the NEC says.

You cannot damage the finished surfaces in the building.

A box behind a screwed in place panel is acceptable, a nailed in place panel is not.

The vanity cabinet is not acceptable as an obstruction.

Either move the box from behind it and use a blank cover plate or put it completely behind the cabinet and cut an access hols in the back (if needed).


 o
RE: junction box blocked by vanity cabinet

That is, in fact, almost precisely what the code says at 314.29. Later, I think in relation to metal boxes, it says, at 314.72 (D):
"Boxes shall be installed so that the wiring is accessible without removing any part of the building..."
There's no mention of "finished surfaces" although, in practice I would assume it's the same thing.
I do appreciate your expertise, but I CAN read. If I'm reading out of context, that would be helpful to know. Thanks.


 o
RE: junction box blocked by vanity cabinet

My immediate recall agreed with that of brickeyee. It comes from the definitions in Article 100. Article 314.29 does not have the word finished.


 o
RE: junction box blocked by vanity cabinet

About the second full sentence in the code is the definition of "accessible" in Chapter 1:


Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.

Any way, regardless of which definition of accessible you are using, it means the same thing. Unless the vanity is an unattached piece of furniture (which due to plumbing they rarely are), it blocking a box does NOT meet the definition of accessible.


 o
RE: junction box blocked by vanity cabinet

"That is, in fact, almost precisely what the code says at 314.29. Later, I think in relation to metal boxes, it says, at 314.72 (D):
"Boxes shall be installed so that the wiring is accessible without removing any part of the building..."
There's no mention of "finished surfaces" although, in practice I would assume it's the same thing.
I do appreciate your expertise, but I CAN read. If I'm reading out of context, that would be helpful to know. Thanks."

The NEC is lik any other legal document when it is adopted.

Words have their 'normal' meaning UNLESS they are otherwise defined.

The NEC defines what 'accessible' means rather explicitly in Article 100, Definitions.


 o
RE: junction box blocked by vanity cabinet

IMO (and I'm not a AHJ), you'd probably be OK if you notched the vanity cabinet so that the receptacle is usable, and there is enough room to work on it reasonably well (unscrew it, remove it, rewire it).

That's a big notch and an ugly one.

I'd say your remuddlers need to put 'er in reverse and take another run at it, with the vanity a few inches to the right or left.


 o
RE: junction box blocked by vanity cabinet

Or move the box.

However either move is going to require professionals which these clowns apparently are not.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here