Ground Wire in Every Conduit?
| | |
Posted by
Danvirsse (
My Page) on
Mon, Aug 22, 11 at 21:09
| We are in the process of rough wiring our 180 yr old home. At the suggestion of our Electrical Contractor, we will be installing 2 large juction boxes (1 in the attic and 1 in the basement) and running each 20Amp circuit to one of these 2 boxes. There will then be PVC conduit with THHN/THWN running from the Juction boxes to the Panel. Of course, the junction boxes will be sized appropriately for the number of conductors housed. Our question is if 2 conduits run from a junction box to the panel due to space constraints and allowable fill capacities, do we need a ground in each conduit or just 1 of the conduits? |
Follow-Up Postings:
RE: Ground Wire in Every Conduit?
| | |
| You must run a ground in the same conduit as the rest of the circuit conductors. |
RE: Ground Wire in Every Conduit?
| | |
| "There will then be PVC conduit with THHN/THWN running from the Juction boxes to the Panel. " You are likely to encounter conductor derating requirements for the large number of current carrying conductors in the home run conduits. |
RE: Ground Wire in Every Conduit?
| | |
| Is there a reason you aren't just putting subpanels in the basement and the second story? Seems a lot easier to pull 1 line than a bunch. It also would make future expansion a lot easier. |
RE: Ground Wire in Every Conduit?
| | |
| Bill - Thanks for the input. I'm not sure why the contractor didn't suggest the subpanels, but I'll ask him. They seem like a good idea, especially since we're going to have to run multiple conduits from each junction box to the panel due to the space constraints and derating. |
RE: Ground Wire in Every Conduit?
| | |
| Can't put a panel in the attic unless there are permanent stairs leading to it. there may not be enough space in the basement location to fit a panel with clearance requirements what they are. |
RE: Ground Wire in Every Conduit?
| | |
I just met with the electrical contractor again tonight and, ionized, you are exactly right. No space in the basement with the appropriate clearances. Ditto the 2nd floor, since it a cape cod style. Guess we're going to be staying with the junction boxes. Thanks to everyone. |
RE: Ground Wire in Every Conduit?
| | |
| Hallway wall on the second floor? The folks who wrote the NEC are less concerned about appearance than about their approach to safety. |
RE: Ground Wire in Every Conduit?
| | |
| Why not cable? Is conduit specifically required in your area? |
Post a Follow-Up
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in.
If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.