Convert 240v to 120v outlet
Posted by sousvide23 (My Page) on
Fri, Aug 27, 10 at 19:56
I am installing a new all gas range from my electric range. Is it possible to change the existing 240v outlet to a 120v outlet in a new position (the new range is specific on the location) - the new position is not too far away from the original location though.
I prefer not running new wires. Is there any changes I'd have to the do at the breaker box as well?
Thanks in advance.
RE: Convert 240v to 120v outlet
Sure, converting a dedicated former 220v range circuit down to 120v is definitely possible. You MUST make changes at the breaker box, do not simply change the outlet itself to a standard 120v outlet without changing from the current double pole breaker to a single pole breaker... you will burn out the entire electrical system/electronics of the new gas range! Some 240v circuits use only two wires and others use 3, If yours has 3, one wire should stay on the neutral bar in the panel and one wire to the new single pole breaker. the third wire will not be used anymore and can be curled up and capped inside the panel. If you have a 2 wire circuit, then detach both wires from the current 2 pole breaker and place one on the neutral bar and the other to the single pole breaker. When changing the outlet in the kitchen, the color of the wire (usually red or black) that you have attached to the single pole breaker will go to the brass colored screw on the new 120v outlet and the wire you have attached to the neutral bar (usually white) should go on the silver screw of the 120v outlet. The wire you capped in the panel will also be capped in the outlet box since it is now "dead".
Now for location...if the existing outlet if fed from below and you will be moving it lower to the floor, you should be fine since you will have enough slack in the wires, however if the opposite is the case you more than likely will need to run new wires. Good luck.
Let me clarifiy something that Scotty says, when he's talking two versus three wires he is not counting the bare or green wire which is the equipment ground. That stays as it is (and connected to the green screw on the new receptacle).
If you have the two wire scenario described above, please mark both ends of the wire you make into the neutral white.
In many panels that are at the main disconnect, there may not be a separate neutral bar (look for where other white wires are connected).
Add on more thing... the wires used for stove wiring will not fit a 120V receptacle, you must pigtail some 12ga wire to each wire in order to fit the receptacle screws. You may have to do the same at the breaker end also, depending on the type and design of the breaker.
And if the existing wiring is aluminum, you'll need to use a rated splicing method.