Electrical Mess - Shared Netural Same Phase

Posted by Mr7o4 (My Page) on
Sun, Aug 5, 12 at 17:27

HELP! I have some issues...

While adding a pantry/closet I decided to rewire my kitchen light/switch, as the BX was too short to where I wanted to put a new switch. I pulled the kitchen light fixture and the drywall was charred, wires burnt, insulation cracking, etc.

I decided to trace out the wiring and replace the entire branch feeding the light (and two outlets). I put a toner on the hot to trace out the circuit, but then found it had some stray voltage on it. Put a meter on it and it read about 20VAC to ground/neutral with the breaker off. So I pulled the dead front on the load center and found that there is a 14/3 wire feeding both the kitchen light / garage circuit and another breaker - both are on the same phase. I killed the other breaker which removed the stray voltage, but I honestly can't find what the second breaker even powers.

Not being an electrician, my question is couldn't the two circuits on the same phase with a common neutral cause the neutral to be overloaded? Most of my wiring is older - late 60's but should be fine in my opinion (BX w/bonding strip). The insulation on the wires to the kitchen light fixture were brittle and cracking, and the drywall around the box was singed. All I can assume is that the circuits sharing a neutral should be on different legs, but I'm not positive on that. I pulled the hots out of the panel and tried to trace them, but they're all over the place - Can anybody with experience tell me why this might have been done in the past?

It's like Pandora's Box opening up this stuff. So many issues - In the attic, any newer circuit the previous owner ran with NM is just pushed into a junction box with the knockout half bent in - no connectors. And wire nuts? Forget 'em! Just twist and tape them together. Almost every switch I pull has blackened wires from arcing because they were so incredibly loose.

It looks like only two 15A breakers serve the majority of the house, with all the splices they did. My load center is an old Wadsworth, and I have no room to split circuits at this time.

Any insight? It's too hot in that attic right now!


Follow-Up Postings:

 o
RE: Electrical Mess - Shared Netural Same Phase

...my question is couldn't tehe two circuits on the same phase with a common neutral cause the neutral to be overloaded? Most of my wiring is older - late 60's but should be fine in my opinion (BX w/bonding strip). The insulation on the wires to the kitchen light fixture were brittle and cracking, and the drywall around the box was singed. All I can assume is that the circuits sharing a neutral should be on different legs, but I'm not positive on that. I pulled the hots out of the panel and tried to trace them, but they're all over the place - Can anybody with experience tell me why this might have been done in the past?

You are correct in concluding that two circuits on the same pole can cause overloading of the neutral. This could be an error dating back to the original panel installation or it could be a situation that was caused by a misguided "reorganization" of the breakers afterwards. Who knows?

[Not that it's hugely important, but the proper term is "pole" or "leg" not "phase" in a 120/240 split-phase system. I'm also assuming that the neutral (in Bx cable!) is the same wire guage as the two hots.]

As for the evidence of heat damage in the proximity of lighting fixtures, that's not an uncommon problem. Your wiring is probably rated for 60C degrees whereas many recent fixtures require wires with 90C insulation. When folks replace fixtures or choose an oversized lightbulb, this pesky detail is very often overlooked.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here