| Im wiring a 1 HP 220v pool pump located next to my house and 25'+ from the pool water.My plan is to run 12-2 UM w/ground to a PVC junction box inside my unfinished bsmt before I punch outside.The pool pump circuit will come off the main(2 pole 20 AMP GFCI breaker) into a 2 pole Intermatic timer and run 40' to the junction box.
My question is can I switch over to THWN from the junction box go through the wall into PVC tubing down to the poolpump outlet(mounted on side of house),220 V 20 AMP rated twistlok receptacle and 3' SJ cord into poolpump motor?? The reason being is Id have to drill through the foundation to account for the 3' requirement of the cord. Thanks for any responses |
Follow-Up Postings:
|
- Posted by manhattan42 (My Page) on Sat, Aug 21, 10 at 11:35
| Everything should be fine except: -SJ cord is not rated for damp locations only. Can't be used in wet locations. -Depending on your Code, you may be restricted to having the pump motor wired using flexible conduit only. (IRC electrical provisions permit twist-lock cords on permanently installed above ground pools only.) |
|
- Posted by manhattan42 (My Page) on Sat, Aug 21, 10 at 18:30
| The above should read: "SJ cord is rated for damp locations only" |
|
- Posted by petey_racer (My Page) on Sun, Aug 22, 10 at 9:40
| I think the term "SJ cord" is generic for flexible cord. Most cords like this are typically "W: rated as well. "-Depending on your Code, you may be restricted to having the pump motor wired using flexible conduit only. (IRC electrical provisions permit twist-lock cords on permanently installed above ground pools only.)" I have never heard of any requirement, even local, that requires a conduit-only connection to a pool pump motor. Of course it may exist somewhere, but in all my years i have never heard of such. |
|
- Posted by manhattan42 (My Page) on Sun, Aug 22, 10 at 13:04
| Petey is somewhat right. Twist lock receptacles are allowed for any permanently installed pool pump motor installation but are only usually found supplied with non-storable type above ground pools. Twist lock receptacles cannot be used with storable swimming pools. Storable swimming pool cords come with their own factory supplied grounded attachement plugs that are required to have a built in GFCI protection device. ----------- |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.