Where can I find proof?

Posted by jscozz (My Page) on
Tue, Aug 21, 12 at 10:43

I know very well that a GFCI does not require a ground to work... but I need to convince an inspector that this is the case. He only sees that it does not trip with his tester... which I know is using the ground to trip it... as opposed to the built in test button that uses the neutral. And I know it is perfectly legal and code compliant to have a GFCI in an old house which does not have aground, in order to meet the 6ft kitchen GFCI code. But the inspector (not electrical inspector... but rental habitability inspector) is asking for proof or statement from an electrician. Is there a section of the NEC that states this is code compliant I can refer him to?


Follow-Up Postings:

 o
RE: Where can I find proof?

Article 406.4 (B) Exception No, 2, 406.4 (D)(2)(b) and (c). The NEC is more definitive than the statement of any electrician. I suspect that the inspector will have difficulty understanding the language. If the inspector was truly worthy of his position, he would already have learned this information of his own volition.


 o
RE: Where can I find proof?

Yes, Bus is right. Make sure you've appropriately marked (the GFCI's often come with labels in the packaging) the protected receptacles with "No Equipment Ground" on all protected receptacles (even the GFCI itself) as well as "GFCI Protected/No Equipment Ground" on any downstream protected receptacles.

Actually both the exception in 406.4(A) and the exception #2 in (B) apply here. I'd highlight both exceptions and the text in 406.4(D)(2). You might be able to get the local electrical inspector to concur which ought to have weight.


 o
RE: Where can I find proof?

If this clown is asking for this he has NO place doing inspections like these.


 o
RE: Where can I find proof?

Thanks for the info. Luckily the electrical inspector let the rental inspector know that it was OK as is. So I did not have to throw the code section at him... thank you all for your help.


 o
RE: Where can I find proof?

My post used the word "volition". While not necessarily incorrect, the better choice would have been "initiative".


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here