Is BX cable sufficient ground in itself?

yazk
13 years ago

Hi,

We have moved into a new house that is a bit of a fixer-upper. We're remodelling the kitchen and need to add a few ceiling lights in bedrooms and the living area.

Most of the existing outlets are 2 prong and looking at the wiring we have BX / armoured cabling with no separate ground wire.

I would like to change out a number of the outlets to 3 prong. Is the ground from electrical box -> metal cable -> house ground, considered 'good enough'?

I'm half thinking I may as well get the electrician to replace everything while he's doing the kitchen electrics and the celiling lights, before we decoreate the house.

Any thoughts??

Thanks.

Comments (8)

  • brickeyee
    13 years ago

    You are actually pretty unlike;y to have actual BX cable.

    Look at the end of a cable in a junction box for a thin metal bonding strip.

    The bonding strip allows the use of the armor on AC cable to be used as ground.

    Real BX does not have a bonding strip.

  • btharmy
    13 years ago

    If it is in fact BX cable without a bonding strip, then no, it is not "good enough" to use the jacket as an equipment ground. My home, built in 1928 and many in the area built pre 1940 or so had 2 prong outlets with bx and knob and tube. I can only assume if the house was trimmed out with 2 prong devices that there was no equipment ground available to begin with.

  • DavidR
    13 years ago

    I don't know what the code called for in, say, the late 50s and early 60s - but I've encountered several houses from that era in which grounded circuits were run to the kitchen and garage, but 2-pin receptacles were fitted.

  • baymee
    13 years ago

    I believe the code allows up to 6 feet of BX in length to act as a ground without a bonding strip.

  • brickeyee
    13 years ago

    Initial versions of NM cable did not have a grounding conductor.

    Later a grounding conductor was added, but is was smaller then the current carrying conductors (around #16-18).

    BX was discovered to have problems with ground continuity using just the spiral armor.

    It was de-listed and not re-introduced until years later as AC cable with a bonding strip.

    While it is possible for the armor on BX to heat up (it is a common demonstration with a Variac to control the applied voltage and make the armor glow red hot) it is still a rare event.

  • mike_kaiser_gw
    13 years ago

    Later a grounding conductor was added, but is was smaller then the current carrying conductors (around #16-18).

    I thought the ground wire looked small but with aging eyes I thought it was my imagination....perhaps not.

  • DavidR
    13 years ago

    IIRC, the original ground in NM was allowed to be 2 sizes (4 numbers) smaller than the current carrying conductors. In #14 cable, a #18 ground was permitted; #12 cable used a #16 ground.

    The method Mike mentions of "bonding" the ground wire to the box is one I've seen many times in work done around 1960. Kind of makes you wonder, eh?