20 amp circuit breaker and wiring

baymee
13 years ago

Forgive me if this has been posted before.

If I am adding a switch and light to a 20 amp circuit, does the light switch, as well as the wiring to the switch and on to the light fixture have to be 20 amp as well? 12 ga. wire?

Comments (21)

  • bus_driver
    13 years ago

    The wire must be 12 gauge. The switch can be of rating less than 20 so long as it is adequate for the load it supplies.

  • baymee
    Original Author
    13 years ago

    Just to clarify, the wire from the 20A receptacle that powers the switch must be 12 ga., the switch can be 15A, and the wire from the switch to the light can be 14Ga?

  • hendricus
    13 years ago

    yes

    yes

    no All wires on a 20 amp breaker must be 12ga.

  • smithy123
    13 years ago

    correct, but you really should be using a 20a switch

  • spencer_electrician
    13 years ago

    No, a 20 amp switch is not needed here, it would be a waste. Unless the light the poster from 2 months ago installed uses more than 1800 watts, a 20 amp switch is not needed.

  • brickeyee
    13 years ago

    "correct, but you really should be using a 20a switch"

    The NEC allows the use of 15 A receptacles and switches on 20 A circuits as long as it is not the ONLY receptacle (and a duplex counts as two) on the circuit.

    If the load is over 15 A on the switch, you would also have to increase the rating of the switch.

    15+ amps of lighting (1800+ watts) is a lot of lighting on a single switch in a residential application (it is not uncommon in large halls (think commercial/church/school).

  • smithy123
    13 years ago

    I stick to whatever size the cb is. What if a rec would be added later down the line saves work. 20a switches also last longer.

  • baymee
    Original Author
    13 years ago

    I had to read what brickeyee said, about 10 times, until it sunk in.

    We are now talking about a circuit that uses 12 ga. wire in its entirety, a 20A circuit breaker, but a mixture of 15A and 20A receptacles and switches. The weak link appears to be the 15A receptacles. This is rather confusing to most people.

  • petey_racer
    13 years ago

    Baymee, you are misreading what Brick is saying.
    The 15A receptacles are NOT a weak link. A 15A receptacle IS rated for 20A feed through.
    The only thing 15A is the slot configuration on the front.

    Smithy, 20A switches do NOT last longer. Heavy duty, or spec-grade, switches do.
    The only reason people think this is because there are no cheap 20A switches. If you buy 15A spec-grade switches they last just as long as 20A spec-grade switches.

  • hexus
    13 years ago

    "I stick to whatever size the cb is. What if a rec would be added later down the line saves work. 20a switches also last longer."

    you aren't going to get very far in this field with your way of thinking....

  • baymee
    Original Author
    13 years ago

    I wasn't aware about the amperage capability of a 15A receptacle being the same as a 20A. Is this stated in the code?

    When you think about it, look at a radio. It plugs into a 15A receptacle, but has tiny wires that wouldn't even support 5 amps, and they never burn up.

    I'm definitely keeping info on this topic.

  • ontariojer
    13 years ago

    it is written on the rec. normally.

  • brickeyee
    13 years ago

    See Table 210.21(B)(3) Receptacle rating for Various Size Circuits.

    It clearly shows that a 20 A branch circuit is allowed to use 15 A or 20 A receptacles.

    210.21.(B)(3) Receptacle Ratings starts off with "Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or where larger than 50 amperes..."

    You have to remember that the #14 15 & #12 20 A limit is not based on the actual wire size and insulation temperature, but one intended to make sure that the most commonly used circuits(15 A & 20 A) have extra margin.

    This is why they can be used at their full rating for motor circuits, hermetic compressors, and start off higher for derating in conduit.

  • baymee
    Original Author
    13 years ago

    Here's a link to a discussion of this issue. It apparently causes problems for more people than me.

    http://forums.mikeholt.com/archive/index.php/t-112623.html

  • smithy123
    13 years ago

    i was arguing with the kauffman's chicken guy because he did not have a 20a plug on his trailer that draws 20a. it is a safety hazard because he could plug it into a 15 amp extension cord. the chicken is good, though.

  • brickeyee
    13 years ago

    "... trailer that draws 20a. "

    Did you measure the current?

    Or just feel to see if the cable was warm?

  • smithy123
    13 years ago

    the trailer has hubbell 20a twist lock connectors

  • smithy123
    13 years ago

    the plugs were p&s knockoffs of hubbell hbl5266c. they had twist lok females rated for 20a/240v, single phase. he said the 5-15 plugs were rated at 20a, but they were marked 15a. he said the 20a plugs were for heavy duty use, but they were for anything draving more than 15a.

  • k27k
    13 years ago

    When I was at a fair i seen that this one stand had A J-BOX MOUNTED TO THE SIDE OF THEIR OVEN!!!!!! I THINK THAT THAT IS A VERY BAD IDEA! The wires inside it are probably not rated for that high of a temp. althought th j-box was metal.

  • smithy123
    13 years ago

    the wires running from the oven were probably rated for that temperature, kyle.