New Circuit Questions

Posted by shay1208 (My Page) on
Sun, Aug 29, 10 at 0:23

I need to add a new 220 volt 40 amp circuit and receptacle to my garage. My panel is listed as being max of 225 amps. I have check with Oncor (power distribution company here in Dallas), and I have 200 amp / 240 volt service. The main disconnect is a dual 60 amp breaker. It is outlined in the picture below. Does this mean I have 120 amp service? If so can I replace the 60 amp dual breaker with a 100 dual breaker to increase my service to 200 amps?

TIA,

Shay

panel


Follow-Up Postings:

 o
RE: New Circuit Questions

NO. DO NOT replace that breaker with a larger one without having an electrician check out your panel.
You have a 200A service. You panel is what is called a split-buss panel. ALL the breakers in the top section are main breakers. You are allowed up to six main breakers. That 60A is the "lighting main".
Split-buss panels are no longer made.

That is also a Zinsco panel. They are notorious for failures and burning up busses (as in the metal rails carrying power to the breakers).

Your best bet would be to have someone replace that panel with a new 200A main breaker panel.


 o
RE: New Circuit Questions

Gosh, I remember replacing that blasted Zinsco panel in my own house. Even finding the big amperage beakers will probably be pricey. It certainly was annoying with those breakers fail (no fire in my case but the circuits with fritz off).

As Petey points out (and I'll just clarify) the top section breakers are not controlled by the 60A. This is how you can get 200A with the 60A "lighting main" below. There's a special dispensation for service disconnects (hokie) that allows this provided all the power in the house can be killed by moving only six handles. In your case (as near as I can see), you've got four tied-together breakers above the lighting main and the main for five. You could put another big circuit on the top section but frankly if I was going to add anything, I'd think about replacing the whole thing with something that's modern.

Getting new Zinsco breakers is getting pricey these days anyhow.
I made some of my neighbors happy when I put my old panel on the street and marked it "free breakers" .


 o
RE: New Circuit Questions

Thank you for the advice. I have read about split bus panels. Any idea what a ballpark figure for a panel replacement would be?


 o
RE: New Circuit Questions

Runs about 2k around here.


 o
RE: New Circuit Questions

Thank you Ron.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here