Lights flickering on 3 pole setup

Posted by E_Hill (My Page) on
Sat, Jul 27, 13 at 22:50

Hi,
Doing a renovation of my attic, and was setting up a 3 pole light circuit with 2 lights, and 2 switches.

power (14/2) -> switch #1 (14/3) -> Light #1 (14/3) -> Light #2 (14/3) -> Switch #2 (14/3)

After a little trouble shooting I got the switches working correctly, but now the bulbs are not lighting up at full illumination and they flicker. Both fixtures are standard cheap porcelain type (they'll be replaced after all the work is done) with CFL bulbs, and neither of the switches are dimmers or lighted.

Would this be a faulty connection? Faulty piece of equipment?

Any suggestions would be appreciated!


Follow-Up Postings:

 o
RE: Lights flickering on 3 pole setup

Would this be a faulty connection? Faulty piece of equipment?

Of those two I'd say that you have them wired incorrectly!

Try this link.

Here is a link that might be useful: 3-Way Switch


 o
RE: Lights flickering on 3 pole setup

You mean 3-way, not 3-pole.

Just a question: WHY would you want to wire it this confusing way? Why not just go from switch to switch with 3-wire???

If you followed that diagram then that is your problem. You CANNOT wire this with 3-wire between the lights. You either need 4-wire or two cables.
Between the lights (besides the ground) you need the two travelers, neutral and switched hot. That is four conductors.
That diagram is TOTALLY wrong. This is what I hate about online diagrams. Folks take them as gospel regardless of source. Any diagrams like this are drawn by someone trying to be nice, or maybe make a buck. We in the trade do not use diagrams, so there are no official stock drawings like that.


 o
RE: Lights flickering on 3 pole setup

Thanks, I got it fixed with that. I guess the original diagram I based it off of was faulty!


 o
RE: Lights flickering on 3 pole setup

So tell us what was wrong. My guess is that the lamps were connected in series.


 o
RE: Lights flickering on 3 pole setup

My original setup had only the 14/3 going between light 1 & 2 (as shown in the diagram I supplied in my first post). I swapped it out for the two strands of 14/2, and now it works perfectly.

As to why did I wire it this way? Well, we already had the first light in place, and then decided that we should add another light in the short hall at the top of the stairs on the same circuit. I was trying to wire it with the leftover wire I had on hand, and none of the lengths would make it from the first switch to the second switch...

Thank you for the help!

Also, thanks for the clarification on pole vs switch.


 o
RE: Lights flickering on 3 pole setup

For many years now, using the "two strands of 14/2" as you describe has been a code violation. NEC 300.3(B) (2011).


 o
RE: Lights flickering on 3 pole setup

Yes! it feels good finally you have discovered the right concept & design


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here