Aluminum wiring and induction cooktop

Posted by twitter007 (My Page) on
Sat, Jul 28, 12 at 22:09

Hi,

I'm planning to replace a electric radiant heat cooktop with an induction unit. Existing wiring is aluminum romex with a 40A breaker. I measured the thickness of wire using a wire gauge and it's 3/16". So it's either a #4 or #6 cable. The new unit is rated at 10.8 KW and requires a 50A circuit.

I read somewhere that a household cooking appliance of up to 12KW can work with a 40A circuit. Can I just connect the cooktop to existing circuit?


Follow-Up Postings:

 o
RE: Aluminum wiring and induction cooktop

Google: appliance hardwired to house aluminum wiring

The link is given in the second item listed.

There is also a Garden Web item further down. "220 etc "

Here is a link that might be useful: AMP Splicing system


 o
RE: Aluminum wiring and induction cooktop

"I read somewhere that a household cooking appliance of up to 12KW can work with a 40A circuit. Can I just connect the cooktop to existing circuit?"

Yes, you are correct.


 o
RE: Aluminum wiring and induction cooktop

Just as importat as the NEC circuit limits are the instalation instructions for the equipment.

If the instructions for the unit say a 50 A circuit is required you must then instal a 50 amp circuit.

The NEC determines what wire gauge are allowed for the circuit.


 o
RE: Aluminum wiring and induction cooktop

I talked to two electricians and got different opinions (just like brickeyee and petey_racer).
First one said (talked to him on phone) it's okay to use the existing wiring since the cooktop will draw more than 10KW only if all 5 burners are turned on at max power which is extremely unlikely. He suggested to not change the breaker so if we ever turned all burners, breaker will trip.

Second one came by and said I can keep existing wiring if it's #4 otherwise it needs to be replaced. Cost would be approx 1400 including 12 hours of labor, 80ft of #6 cu wire and 50A breaker.

If replacing the wiring cost few hundred dollars, I would do it in a heartbeat but need to research more before spending 1500 dollars on it.

To further compound the matter, my panel is Federal Pacific stab-lock.

decisions... decisions...


 o
RE: Aluminum wiring and induction cooktop

"The new unit is rated at 10.8 KW and requires a 50A circuit."

If the installation instructions say "requires a 50A circuit" you do not have a choice.

You need to run conductors large enough for a 50 amp circuit protected by a 50 amp breaker.

The NEC requires manufacturer's installation instructions to be followed.
They supersede any NEC rules in this case.

The NEC still controls the wire size required, but you need a 50 amp circuit.

The NEC does allow for diversity for multiple stoves, but you only have one device.


 o
RE: Aluminum wiring and induction cooktop

here's something to think about..
voltage drop..while this will not cause the cooktop to draw more current like a motor. but it will reduce the heat output.this could lead to turning up the burners..hum..
maybe there is another reason besides CODE to use the proper wire size..or LARGER! but use a 50amp breaker(say 4ga copper instead of 6ga).. at 80ft at 50amp is #6 large enough? just asking I don't know the numbers off the top of my head..the NEC and other wire gauge tables exist. look them up.

other dumb question..what's the voltage? 240V or 380v?

-dkenny


 o
RE: Aluminum wiring and induction cooktop

"I'm planning to replace a electric radiant heat cooktop with an induction unit. " OP

"voltage drop..while this will not cause the cooktop to draw more current like a motor. but it will reduce the heat output.this could lead to turning up the burners..hum.. "

Not necessarily true for an induction cook-top.

One of the first things most do with the the incoming power is turn into DC, to then be chopped to high frequency AC (many thousands of cycles per second) to produce the fast varying magnetic field for induction heating.

Depending on the power supply design chosen the current may increase when voltage declines.


 o
RE: Aluminum wiring and induction cooktop

To further compound the matter, my panel is Federal Pacific stab-lock.

decisions... decisions...

The FIRST decision to make is to REPLACE the Federal Pacific panel!

Then start from there!


 o
RE: Aluminum wiring and induction cooktop

Grouped of induction hobs are typically are not capable of putting out equal to the additive total power of the hobs. If you turn then all on to their highest setting, the power will be chopped to some or all of them.

Just an example to make it clear. If you want to boil a large volume of water in two pots on a 4-hob cooktop, you need to know which pairs of hobs are on the same power supply and choose the hobs accordingly. Typically the hobs are paired on two power supplies. If you choose two on the same supply, you might only get 70-80% of the rated power. Probably, it will be in the manual for the appliance.

If your power supply to the cooktop is not optimal, you may get less than you can from the appliance. Few people will notice any difference, but if you are a heavy-duty cook, you might.


 o
RE: Aluminum wiring and induction cooktop

Get rid of the F-P panel.

While old ones did not have problems, as the brand name was bought and sold defective breakers ended up being made and installed.

The worst offenders are 240 V double pole breakers that fail to open, or only open one side in an overload.

The overall connection of the individual breakers to the bus in the panel also left much to be desired, especially for heavy loads.

If the manufacturer's installation instructions require a circuit size, you do not get to adjust that downward based on the nameplate load of the equipment.

The electric code requires you to follow the manufacturer's instructions.


 o
RE: Aluminum wiring and induction cooktop

"voltage drop..while this will not cause the cooktop to draw more current like a motor. but it will reduce the heat output.this could lead to turning up the burners..hum.. "

Not necessarily true for an induction cook-top.

um..yes..its true..
the cooktop controls the strength of the magnetic field..it doesn't output more if 2 pans are placed on the same burner. the equivalent of loading a motor for no-load to full load..at least that's my thinking..

-dkenny


 o
RE: Aluminum wiring and induction cooktop

"um..yes..its true.. "

It depends on how the DC supplies in the unit are designed.

MANY DC supply designs will pull more current under low voltage condition to meet their output load.

And you are wrong about many motors.

Universal motors (the ones with brushes) will just slow down, and voltage control can be used to adjust their speed.

Newer stepper motors have a DC supply and may not speed control with voltage unless designed that way.

Induction motors will draw increased current to meet the load they are driving under low suplly voltage conditions.

This can lead to overheating of the stator windings and the motor shutting down from overheat.

A lightly loaded induction motor (single or even 3-phase) CAN have the voltage trimmed back until the current starts to rise to save power.

It is a risky thing since if the motor load increases the motor will pull more current until the voltage is adjusted back up.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here