| I'm doing work to finish a section of my basement (all permits properly pulled!). At my rough electric inspection, the inspector alerted me to the new bonding requirements for the flexible gas lines in my house (CSST). I understand the requirements, but have a couple of additional questions.
1. He noted that 6awg wire is required for my situation. Because the gas entrance is at the other end of my basement from the common ground, I intend to use insulated THHN/THWN wire. I don't like the idea of 60 feet of bare wire acorss my basement. Stranded THHN/THWN seems much more common and appears to meet the necessary specs. Does NEC say whether I should use stranded or solid for bonding? 2. I seem to recall that single wires need to be in a conduit. Does code require that I put this single insulated bonding wire in conduit? The entire run will be accessible, if that matters. Thanks very much for the information. |
- Posted by petey_racer (My Page) on Sun, Jul 25, 10 at 22:59
| Stranded or solid, bare or insulated. it's your call. No conduit is required or needed. Just keep it out of harms way. I am not sure why the idea of bare wire scares you. This is typical for any bond or grounding electrode conductor wire. |
- Posted by petey_racer (My Page) on Sun, Jul 25, 10 at 23:00
- Posted by bobinbaltimore (My Page) on Mon, Jul 26, 10 at 18:04
| Thanks, Petey. Bare wire doesn't scare me, but I like the idea of having a jacket so that in the case of a fault there is less likely to be inadvertent energizing of metal in incidental contact with the ground (like sheet metal used in creating cold air returns between joists that are along the path of this wire). Call it a little comfort level, that's all. |