| I'm a little bit baffled on this... whether or not it's allowed...
Original service is 100A - HVAC is currently a 90A breaker in that box...
|
Follow-Up Postings:
|
- Posted by bus_driver (My Page) on Thu, Jul 26, 12 at 21:40
| I believe that Article 230.71(A) of the NEC (2011) permits the arrangement you suggest. This Article provision is not new to the code by any means. If your inspector disagrees, this one is worth an appeal to his superior and higher if necessary. |
|
- Posted by bus_driver (My Page) on Fri, Jul 27, 12 at 8:17
| To explain a bit more, in the plan you propose, the meter/load center is the service, the panels in the mobile home are then subpanels. Be sure to have the neutrals bonded only at the service, not in the subpanels. |
|
| The first disconnect is a main, and all panels after it are sub-panels. A main has a 3-wire feed (H-H-N) and a grounding electrode system. The main is the only place grounds and neutral may be connected. Subs require a four wire feed (H-H-N-G) and isolated grounds and neutrals in the sub-panels. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.