bathroom lights on GFCI ?

Posted by hoosierdoc (My Page) on
Sun, Jul 10, 11 at 20:49

I wired my basement and followed what I thought was code. Our inspector (selling it) said that the lights cannot be on the GFCI circuit. I have a normal 20A breaker that feeds this bathroom only. The outlet is a GFCI one and it feeds a vent fan, light, and shower light.

Isn't this one of the valid code installs if you have a dedicated 20A circuit?


Follow-Up Postings:

 o
RE: bathroom lights on GFCI ?

You are perfectly within code here. Do not listen to this hack inspector. He is wrong.


 o
RE: bathroom lights on GFCI ?

Yes, as far as the NEC is concerned as long as the circuit feeds only that bathroom you are allowed to put the lights and fan on the same circuit. NOWHERE does the NEC prohibit what you can put on a GFCI, there are things you are not required or otherwise allowed to NOT put on a GFCI.

Some fans and light fixtures actually recommend/require GFCI (for wet/damp areas).


 o
RE: bathroom lights on GFCI ?

I assume this is the house inspector and not an electrical inspector?

A dedicated 20amp circuit can be used for the bathroom receptacles and lights. Your shower light should be GFCI protected. If you fan is above a wet area, it should be GFCI.

In an ideal world where cost isn't a factor and you have unlimited breaker space available, it would be nice for the bath light to be on a separate lighting circuit. That way, if a hair dryer trips, it doesn't knock out the lights too. That is a convenience factor though, not a safety factor.


 o
RE: bathroom lights on GFCI ?

A shower light CAN be GFI protected. "Should" and "must" are subjective words here.


 o
RE: bathroom lights on GFCI ?

The shower light is required to be GFCI protected if the manufacturer's instructions say it is required for the application. Otherwise it is optional.


 o
RE: bathroom lights on GFCI ?

And I for one have never seen this as a requirement.


 o
RE: bathroom lights on GFCI ?

I'm in the middle of multiple bathroom remodels, and every shower light kit I've looked at has a GFCI requirement. It seems to be pretty common. It certainly is required on the 2 I've purchased this year.


 o
RE: bathroom lights on GFCI ?

To clarify, I'm asking mainly about the light above the sink. The light above tub requires GFCI. I don't think it changes things but wanted to be sure.

Thanks for the guidance!


 o
RE: bathroom lights on GFCI ?

Billl, I've never seen a "shower light kit" before, let alone one that required GFI protection. What brand are they?

I will say, I have seen a couple of steam room specific lights that did require GFI protection.


 o
RE: bathroom lights on GFCI ?

I don't know of any situation where code prohibits something from being protected by a GFCI. There are a few situations where it is discouraged, such as a circuit dedicated to a refrigerator.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here