Gentran transfer switch L14-30

Posted by diy_rook (My Page) on
Wed, Jul 31, 13 at 20:37

Electric newbie here..I was recently given a generator and my house always had a Gentran transfer switch (Gentran 30216) that has a L14-30 inlet. My garage has a receptacle that feeds directly to the Gentran.

My problem is that the new generator (Devilbiss GB5000 with a Briggs Genpower 10.0) doesn't have a L14 out and has what I think is Nema 6-20. Am I able to come up with a cord with a 6-20 three prong on one side and a 4 prong L14 on the other end?

Thanks in advance.


Follow-Up Postings:

 o
RE: Gentran transfer switch L14-30

Sorry, but no. You CANNOT use that generator to backfeed a home.
You have a 120V receptacle and a straight 240V receptacle, but not a 120/240V rated receptacle you need.

Some will say jury-rig it and combine the two you have but no way in hell I would do that. It's just not worth it.


 o
RE: Gentran transfer switch L14-30

Ok - Even though it would be sending 240 to the Gentran transfer switch which then has 4 15 amp circuits for 120 and a 220? I thought I could backfeed that switch with the 240 alone and the Gentran switch would determine the 220 or 120? I'm not backfeeding directly to my main box.

Thanks


 o
RE: Gentran transfer switch L14-30

It doesn't matter.
You CANNOT get 120V from 240V without a neutral, and your 240V receptacle on the genny has NO neutral. That is the problem.


 o
RE: Gentran transfer switch L14-30

As pointed out, those generator will not work and there's no way to "kludge" it so it does. It's not just a connector issue, there's no center tap on the 240 output side to make the 120/240 work.


 o
RE: Gentran transfer switch L14-30

Thank you both for the responses. Looks like I'll have to sell this one and get a new one.

What would be the minimum size gen to power a 6 switch transfer switch? 4 at 120 with 15amp the 2 combined for my well pump at 220.


 o
RE: Gentran transfer switch L14-30

The well pump could be a problem- depends on the HP. Mine will JUST BARELY start on a 4000/4400 generator. Almost stalls the generator.
Buy 6500 or larger.


 o
RE: Gentran transfer switch L14-30

Don't guess at the generator output needed to operate the well pump and possibly purchase what you can't use a second time. If you do not have the specifications for the well pump motor, attempt to locate the manufacturer's name and model number of the pump motor. The manufacturer should be able to give you both the start-up and run wattage of the motor. The start-up wattage may be as much as 2 to 3 times that of the run wattage after start-up.

If all else fails have a master electrician test the well pump/motor wattage on the circuit during start-up. It should take him 10 minutes to accurately answer your question.


 o
RE: Gentran transfer switch L14-30

You could use that generator if you installed an L14-30 outlet on it . If you aren't going to use the 240v plug on the generator, remove that outlet and replace it with the L14 outlet. Pull the neutral from one of the 120v outlets.easy piesy.


 o
RE: Gentran transfer switch L14-30

Double posted

This post was edited by Auger01 on Sun, Aug 18, 13 at 23:57


 o
RE: Gentran transfer switch L14-30

Sorry Auger, but you're completely wrong on this. You make the unwarranted assumption that the grounded side of the 120V receptacles on this generator is the center tap of the 240V coil. This is ****NOT**** the case for this generator. There is no center tap on the 240 side to tap into.


 o
RE: Gentran transfer switch L14-30

Somebody is wrong, but it is not me. Here is a wiring diagram of a GB5000. The 240 IS center tapped for the 120 volt.


 o
RE: Gentran transfer switch L14-30

Excellent - thanks for the info Auger01. So I ordered a L14-30 receptacle to install on this generator. Even though the genset is only 20Amp, this is ok right? So wire #3 (neutral from the left 120 side) for my L14-30r right?

This post was edited by diy_rook on Thu, Aug 22, 13 at 10:38


 o
RE: Gentran transfer switch L14-30

"wire #3 (neutral from the left 120 side) for my L14-30r right?"
The confusion about which wire is one of the reasons I made no suggestions earlier.
Suppose that we post precisely our suggestions for the generator. But do we have any confidence that the hookup at the other end will be done correctly? I don't. And a wrong hookup at any point could be disastrous.
Based on what I have seen thus far, it is best to just leave it alone.

This post was edited by bus_driver on Thu, Aug 22, 13 at 19:07


 o
RE: Gentran transfer switch L14-30

Understood - definite newbie here but I plan on having help. The other end is a L14-30 inlet in my garage that was previously installed at my house which feeds into the transfer switch directly. That end is done.


 o
RE: Gentran transfer switch L14-30

Connect your neutral wire to stator lead 2 - 3 or wire 6 -7 or either of the silver terminals on the 120 volt outlet. Post a picture of what you have if you are not sure. Good luck.

The 30 amp is fine.

Edited to clarify stator leads vs wire numbers.

This post was edited by Auger01 on Fri, Aug 23, 13 at 5:22


 o
RE: Gentran transfer switch L14-30

Bad advice.


 o
RE: Gentran transfer switch L14-30

Lesson learned. When responding to bad advice, copy and paste the bad information into the reply in case of later editing.


 o
RE: Gentran transfer switch L14-30

Maybe instead of just saying "bad advice" bussdriver, it might be more helpful to clarify what exactly was wrong with the advice and specifiy the right way to do it.

This is a forum where people seek help with thier projects. The OP has a basic grasp of the concepts involved so I have no problem giving him a push in the right direction. If the only answer you care to give is basically "I know the right way to do it, but I am not going to tell you because you are too dumb to do it correctly", then perhaps your time might be better spent elswhere.


 o
RE: Gentran transfer switch L14-30

My advice was to not pursue that project further. But creating a potentially fatal situation demanded a response.

This post was edited by bus_driver on Fri, Aug 23, 13 at 21:56


 o
RE: Gentran transfer switch L14-30

Ok so I am going to remove the 240 outlet and install the new L14-30 receptacle. black circled (L1), combine both red circled (L2), green (ground), then connect new wire as neutral and tie into #6 (orange)? Is that right?


 o
RE: Gentran transfer switch L14-30

That looks correct.

To make it look neat, you can drill a hole in some .045" -ish aluminium sheet stock from the home center to secure the L14 outlet to and then screw the aluminium to the existing cover.


 o
RE: Gentran transfer switch L14-30

Excellent - I will get it going soon and will post an update. Thanks again Auger01 for the help.


 o
RE: Gentran transfer switch L14-30

OK I did the wiring - here is what I have now. I haven't tested it as I need to do some routine maintenance to the generator first. Please let me know if you see any errors. I used wire nuts and used some 12awg blue wire I had as a pig tail to the new L14 receptacle.


 o
RE: Gentran transfer switch L14-30

The connections look correct, but check it with a multimeter when it is running anyway. Those wire nuts make me nervous. They are going to have to endure alot of vibration. They might work, but they weren't really designed for this application. Here is an alternative connector:

http://www.amazon.com/Lockitt-POSI-TWIST-Assortment-connectors-10-26/dp/B00CMC99EW

Good luck and let us know how it works.


 o
RE: Gentran transfer switch L14-30

All systems go! Auger01 - thanks a lot for the assistance through the process! If I hadn't done this - as much as I wouldn't want to I would've been forced to use the frowned upon backfeed but now this will work perfectly for me and safe for everyone. I tested with the multimeter and both 120 and the 240 are reading properly. It's not the prettiest looking right now as you can see. I'm going to cut a plate like you suggested to clean it up a bit.

It's great to be able to post an issue like this and find a solution. I scoured the internet and couldn't find much info on how to do this so hopefully this thread will help other as well.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here